Re: Extending shore power cable

The place to be worried about a shore power connection failing is at the pedestal. Maybe we should hard wire that.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-08-2017, 08:26   #32
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Extending shore power cable

Quote:
Originally Posted by sailorboy1 View Post
I need a longer shore power cable, will2 standard cables plug together?.
Yes, you can plug two shorepower cables together to make a longer cable and it won't change from a 30 amp cord to a 20 amp cord. There will be an additional voltage drop but no more than if you bought a longer cord to begin with.

I'm not suggesting that someone string three 50' cords together to make a 150' cord, but for reasonable lengths, you'll be just fine.

Theory tells us the shorter the cable from the dock to the boat, the better. I carry two cables, a shorter one and a 50' one. If the shorter one will reach, that's the one I use. Sometimes I need the 50' cable and once or twice I've had to use both as you describe.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 19-08-2017, 09:05   #33
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Extending shore power cable

How much current it can carry depends on how much of a voltage drop you are willing to accept. You won't know ahead of time how much this is until you try it. Some connectors have different amounts of voltage drops than others, even identical connectors.

The voltage drop over a given length of wire is easier to predict, but even that is not 100% predictable.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 19-08-2017, 09:18   #34
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Extending shore power cable

Quote:
Originally Posted by rwidman View Post
...you can plug two shorepower cables together to make a longer cable and it won't change from a 30 amp cord to a 20 amp cord. There will be an additional voltage drop but no more than if you bought a longer cord to begin with...
Not true. You can expect a voltage drop at each set of connections.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 19-08-2017, 09:38   #35
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Extending shore power cable

Quote:
Originally Posted by rwidman View Post
Yes, you can plug two shorepower cables together to make a longer cable and it won't change from a 30 amp cord to a 20 amp cord. There will be an additional voltage drop but no more than if you bought a longer cord to begin with.



I'm not suggesting that someone string three 50' cords together to make a 150' cord, but for reasonable lengths, you'll be just fine.



Theory tells us the shorter the cable from the dock to the boat, the better. I carry two cables, a shorter one and a 50' one. If the shorter one will reach, that's the one I use. Sometimes I need the 50' cable and once or twice I've had to use both as you describe.

A well designed longer cord will use bigger wire to compensate for the extra voltage drop. So a 50 foot cord is usually not the same as 2 25 foot cords plugged together.
transmitterdan is offline   Reply With Quote
Old 19-08-2017, 13:26   #36
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Extending shore power cable

I'm all for the silicone grease myself, I keep a tube or two of Dow Corning DC4 on board, I keep shore power cords plugs well greased, cause I'm cheap. Keep them greased and you will only replace them when they get so old and the insulation so hard you can no longer roll them up to store them, not because they overheated and burnt the ends.
Grease prevents corrosion, corrosion is of course high resistance, high resistance obviously causes heat and low voltage.
I even keep my Smart plug greased
a64pilot is offline   Reply With Quote
Old 19-08-2017, 14:16   #37
Registered User
 
flyingfin's Avatar

Join Date: Oct 2016
Location: Cape Haze,FL
Boat: Carver,Cobia,Nacra, Columbia
Posts: 815
Re: Extending shore power cable

Quote:
Originally Posted by sailorboy1 View Post
The place to be worried about a shore power connection failing is at the pedestal. Maybe we should hard wire that.
Too many people in this blog seem to be shooting from the hip
Y'all need to read the National Electrical Code Article 555

(1) Enclosures. Receptacles intended to supply shore power to boats
must be part of a listed marina power outlet enclosure, be installed
in listed enclosures protected from the weather, or in listed weatherproof
enclosures. The integrity of the assembly must not be affected
when the receptacles are in use with a booted or nonbooted attachment
plug/cap inserted.
flyingfin is offline   Reply With Quote
Old 19-08-2017, 15:20   #38
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Extending shore power cable

What's that got to do with plugging cords into each other
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-08-2017, 16:05   #39
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Extending shore power cable

Quote:
Originally Posted by Terra Nova View Post
Not true. You can expect a voltage drop at each set of connections.
Sure. A half a volt perhaps.

We are talking about supplying power to a boat. A practical real life application not an electrical theory question.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 19-08-2017, 16:12   #40
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Extending shore power cable

Quote:
Originally Posted by transmitterdan View Post
A well designed longer cord will use bigger wire to compensate for the extra voltage drop. So a 50 foot cord is usually not the same as 2 25 foot cords plugged together.
None I've ever seen. 30 amp cords are #10 wire.

Consider this: When wiring a house does the electrician use heavier gauge wires for circuits that are further away from the electrical panel?

Now consider this: The wire run from the marina's panel to your slip is already several hundred feet. What difference does another twenty five feet make?
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 19-08-2017, 16:14   #41
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Extending shore power cable

Quote:
Originally Posted by sailorboy1 View Post
The place to be worried about a shore power connection failing is at the pedestal. Maybe we should hard wire that.
I can't even begin to list the things that are wrong with that idea!
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 17-11-2017, 16:36   #42
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Extending shore power cable

It’s been months now and the connection between the cables hasn’t gotten any moisture in it or had the breaker trip. That’s the fact.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 17-11-2017, 17:14   #43
Senior Cruiser
 
BlackHeron's Avatar

Join Date: Jan 2016
Boat: Bathtub
Posts: 889
Images: 19
Re: Extending shore power cable

Quote:
Originally Posted by rwidman View Post
None I've ever seen. 30 amp cords are #10 wire.

Consider this: When wiring a house does the electrician use heavier gauge wires for circuits that are further away from the electrical panel?

Now consider this: The wire run from the marina's panel to your slip is already several hundred feet. What difference does another twenty five feet make?
Yes, in fact we do.

Voltage drop and wire length are taken into consideration when pulling branch circuits (as well as feeder circuits to panelboards.) This is not so much a big deal in houses as most houses are not large enough to have many problems except some McMansions and real mansions when distances start growing quite large. In the commercial world you bet yo buttocks we need to upsize the wire for longer runs. Often we will pull larger gauge wire out to a junction box from the panel, and then run in the walls with smaller wire to achieve minimum voltage drop numbers (see below.) So a 20A circuit that is 150' from the panel may get #10 wire in the "home run" run underground or overhead to a junction box 100' away and then dive into the walls with #12 for the last 20-50 feet to the individual receptacles.

Voltage drop is function of wire size, circuit voltage, distance round trip, and most importantly current as it is a variable that we can only control by maximum fuse size, so we need to size wire for the maximum of the overcurrent device.

The NEC requires that feeders to panels be sized to allow for a calculated voltage drop of no more than 3%, and that branch circuits to be sized to have a voltage drop of no more than 3% as well -but the combined calculated voltage drop of the feeders plus the branch circuits may be no more than 5% in any circuit.
BlackHeron is offline   Reply With Quote
Old 23-11-2017, 09:45   #44
Marine Service Provider

Join Date: May 2011
Location: Cruising Mexico Currently
Boat: Gulfstar 50
Posts: 1,979
Re: Extending shore power cable

I once needed to have shore power 200' from the outlet. Rather than buying a bunch of 50' shore power cords I bought a spool of Royal SOOW 10 ga 3 conductor wire and put my own connectors on it.

There was a 6 volt drop when running a 1500 W heater.

I still have the cable is anyone wants to buy some (in the PNW)
evm1024 is offline   Reply With Quote
Old 23-11-2017, 10:26   #45
Senior Cruiser
 
BlackHeron's Avatar

Join Date: Jan 2016
Boat: Bathtub
Posts: 889
Images: 19
Re: Extending shore power cable

For something as long as 200' and for a semi-longterm temporary installation I'd be tempted to get 6-6-6 overhead aluminum triplex wire and run it on the ground in 1-1/4" PVC and then hardwire it at the source and build a temporary pedestal. I might consider running it overhead if there was available structure to string it safely.

Perhaps maybe use a 20A or 30A GFCI breaker in an enclosure at the tap to ensure safety along the feeder if it is a high traffic area.
BlackHeron is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
extending Nasa Easy Navtex aerial cable Ketchcalimbo Marine Electronics 4 05-02-2016 06:18
Shore Power Cable Short Circuit ? Alecadi Electrical: Batteries, Generators & Solar 33 07-09-2011 09:10
Ship-to-Shore Power Cable svrevelations Electrical: Batteries, Generators & Solar 16 28-08-2011 19:26
Extending Radar Cable bobs Marine Electronics 34 24-04-2011 19:20
Two Amp Feedback to Shore Power Cable - Help! denmanislander Electrical: Batteries, Generators & Solar 38 29-03-2010 07:57

Advertise Here


All times are GMT -7. The time now is 06:54.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.