Old 25-06-2009, 17:33   #1
Registered User
 
bill good's Avatar

Join Date: Oct 2006
Location: Brisbane Australia
Boat: sold Now motor cruiser
Posts: 692
Electrolysis

Just want to get an idea from anyone out there that could advise me why the earth on the AC circuit should not be via something like a starting capacitor to ensure DC cannot get involved & hence not have electrolysis problems on boats. (not considering RF) It would seem a viable alternate to galvanic isolators.

Regards Bill
bill good is offline   Reply With Quote
Old 25-06-2009, 19:19   #2
Registered User
 
Christian Van H's Avatar

Join Date: Oct 2008
Location: Princeton, NJ
Boat: Challenger Anacapa 42
Posts: 2,097
Images: 57
If I'm not mistaken, you've just reinvented the Galvanic Isolator. It's caps I believe, in them there boxes...
__________________
www.anacapas.com

Here's to swimmin' with bowlegged women!
Christian Van H is offline   Reply With Quote
Old 26-06-2009, 09:43   #3
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,734
Not caps--its diodes, which only conduct when the voltage gets over 0.6 volts.
donradcliffe is offline   Reply With Quote
Old 26-06-2009, 11:12   #4
Registered User

Join Date: Jan 2005
Location: Seattle area (Bremerton)
Boat: C&C Landfall 39 center cockpit "Anahita"
Posts: 1,077
Images: 6
Two diodes

Actually there are four diodes total; two in series paralleled with two others in series "facing" the opposite direction. If only one diode is used in each leg then the 0.8 to 0.9 Volt (approx.) developed by zinc-to-stainless (shaft, for example) potential would cause a galvanic isolator to conduct and waste the zincs.
__________________
"I don't think there'll be a return journey Mr. Frodo". Samwise Gamgee
Rick is offline   Reply With Quote
Old 26-06-2009, 11:30   #5
Registered User
 
Christian Van H's Avatar

Join Date: Oct 2008
Location: Princeton, NJ
Boat: Challenger Anacapa 42
Posts: 2,097
Images: 57
Quote:
Originally Posted by donradcliffe View Post
Not caps--its diodes, which only conduct when the voltage gets over 0.6 volts.
My bad! What extra components do they add to make them "failsafe" for the ABYC?
__________________
www.anacapas.com

Here's to swimmin' with bowlegged women!
Christian Van H is offline   Reply With Quote
Old 26-06-2009, 14:23   #6
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,534
The fail safe GIs utilize extremely rugged components and the unit is tested and certified by a third party. The testing protocol sorts out the contenders from the pretenders.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 29-06-2009, 05:32   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,384
Images: 241
Quote:
Originally Posted by CharlieJ View Post
The fail safe GIs utilize extremely rugged components and the unit is tested and certified by a third party. The testing protocol sorts out the contenders from the pretenders.
A “Fail-Safe” galvanic isolator will “fail closed-circuit”; insuring that the shore power safety ground wire is maintained through the isolator, even in the event of isolation failure.

The criteria for galvanic isolators is defined by the American Boat and Yacht Council (ABYC) recommended standard A-28, which has recently been revised. This standard has a publication date of July 2008 and an effective date of July 2009.
Due to recommendations to the A-28 galvanic isolator standards committee concerning the need to retain safety grounding under all conditions, as required by the U.S. National Electric Code for all similar applications outside of A-28, this standard now makes provision for fail-safe galvanic isolators.
To be considered "fail-safe," an independent laboratory must confirm that the isolator will either remain fully functional or remain a permanent, effective grounding path if it fails when subject to the maximum current rating.
Per the new A-28 standard, galvanic isolators meeting the fail-safe requirement will not require a monitoring system since the integrity of the grounding wire will not be compromised should the isolator fail.
All galvanic isolators not meeting the fail-safe criteria will still require a monitoring system to alert the boat owner that their grounding system may be compromised.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
electrolysis


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Leaking and Electrolysis... svHyLyte Electrical: Batteries, Generators & Solar 34 15-04-2021 08:44
Electrolysis Bonding Question Beausoleil Electrical: Batteries, Generators & Solar 35 07-01-2011 05:41
Yanmar 3GM30F Engine Electrolysis Xtofinooic Engines and Propulsion Systems 8 12-06-2010 07:08

Advertise Here


All times are GMT -7. The time now is 20:01.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.