I was checking our wiring had an issue with a gauge light. And noticed the feed wire to our navigation lights switch is warm. Yes our nav lights are on we are doing an overnight. The wire is about a #8 maybe a 6. Is this normal? It wasnt red hot but fairly warm. Not a place to be concerned miles offshore in the dark...
Dulcesuenos is offline   Reply With Quote
Old 09-05-2013, 17:55   #2
Registered User

Join Date: Apr 2006
Posts: 4,413
Re: Electrical question help please!

#6 of #8 awg for lighting an instrument? That's insanely thick.
Sandero is offline   Reply With Quote
Old 09-05-2013, 18:07   #3
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Its whatever size fits a yellow butt splice connector.
And it's the feed wire for the nav lights switch, theres a mid mast light two forward running lights and a stern running light 4 lights total about 35+' apart biggest concern is should the wire feeding the switch be warm?
Dulcesuenos is offline   Reply With Quote
Old 09-05-2013, 18:09   #4
Registered User

Join Date: May 2010
Location: Elsewhere on the Water
Posts: 579
Re: Electrical question help please!

For an 8 or 6 ga wire to get warm would require 40 amps, or more flowing through it. Could the heat have come from something else? I would verify the size of the wire, and put an amp clamp on it to read the current flow. If there is that much current in it surely there is more than nave lights involved.
St. Elsewhere is offline   Reply With Quote
Old 09-05-2013, 18:12   #5
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Maybe its a #10 wire then.
Dulcesuenos is offline   Reply With Quote
Old 09-05-2013, 18:14   #6
Registered User
 
Kettlewell's Avatar

Join Date: Jul 2006
Location: Massachusetts
Boat: Finnsailer 38
Posts: 5,271
Re: Electrical question help please!

Yellow connectors are usually for 10-12 gauge wire. If they are regular incandescent bulbs they could all be around 25 watts or 2 amps each, meaning a total of 8 amps. It would be worth it to put an amp meter on the line with the lights on to see what it reads, and do the same with the lights off.
__________________
JJKettlewell
Kettlewell is offline   Reply With Quote
Old 09-05-2013, 18:17   #7
Registered User

Join Date: Feb 2013
Location: Oregon
Boat: Seafarer36c
Posts: 5,563
Re: Electrical question help please!

Where are you? Perhaps it's hot out. You should place a cold beer in one hand and a #10 wire in the other.
model 10 is offline   Reply With Quote
Old 09-05-2013, 18:21   #8
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Ty kettleworth, lol Guy, were off Pine island heading to our new berth in the keys.
Dulcesuenos is offline   Reply With Quote
Old 09-05-2013, 18:28   #9
Registered User
 
Ziggy's Avatar

Join Date: Apr 2008
Location: U.S., Northeast
Boat: Currently boatless
Posts: 1,643
Images: 2
Re: Electrical question help please!

3 incandescent nav lights could draw as much as 8A in total (25W each).
Yellow insulated terminals are usually for AWG #10 or #12 wire.
I could definitely see how a #12 wire could get warm.
__________________
... He knows the chart is not the sea.
-- Philip Booth, Chart 1203
Ziggy is offline   Reply With Quote
Old 09-05-2013, 18:41   #10
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Western Caribbean
Boat: 38/41 Fountains pajot
Posts: 3,060
Images: 4
Quote:
Originally Posted by Ziggy View Post
3 incandescent nav lights could draw as much as 8A in total (25W each).
Yellow insulated terminals are usually for AWG #10 or #12 wire.
I could definitely see how a #12 wire could get warm.
Is it a concern?
Dulcesuenos is offline   Reply With Quote
Old 09-05-2013, 19:15   #11
Registered User

Join Date: May 2010
Location: Elsewhere on the Water
Posts: 579
Re: Electrical question help please!

Quote:
Originally Posted by Dulcesuenos View Post
Is it a concern?
At 8 amps a #12 wire should not get warm. If it is quite warm the concern would be that current is going somewhere else too. If it is not real hot the concern is not fire safety, but if it is drawing 20 amps (the level where a #12 gets warm) the battery is going down a lot faster than it should for running nav lights.
St. Elsewhere is offline   Reply With Quote
Old 10-05-2013, 10:05   #12
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 361
Re: Electrical question help please!

12 awg wire will carry 23 amps for 40 feet (or more) and stay at ambient temperature.
Zil is offline   Reply With Quote
Old 10-05-2013, 10:14   #13
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,513
Re: Electrical question help please!

Probably a #10. A little warm is not the end of the world. The best fix may be to go to more energy efficient bulbs in your lights.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 10-05-2013, 10:32   #14
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,392
Re: Electrical question help please!

Is there a terminal connector or a switch or circuit breaker near where you are feeling the heat?

It is possible you have some unwanted resistance (corrosion etc) which is getting hot and the heat is travelling along the wire. Run your hand (carefully & slowly) along the wire in either direction to see if the temperature changes at any point.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Old 10-05-2013, 10:40   #15
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: Electrical question help please!

Quote:
Originally Posted by Zil View Post
12 awg wire will carry 23 amps for 40 feet (or more) and stay at ambient temperature.
Actually, any wire with a current must be above ambient temperature. Temperature rise will be proportional to I^2*R. Actual temperature rise will depend on effectiveness of losing the generated heat (i.e., in free air, in conduit, in a wire bundle, type of insulation etc.).

For 12 AWG a simple calculation (with assumptions) is:

Temp rise (in C) = I^2 * 0.0365

for 10 AWG use 0.0208
Dennis.G is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 16:01.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.