Old 19-09-2017, 17:48   #1
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,044
Did Victron BlueSolar Kill My Batteries?

I installed a Victron BVM-700 battery monitor, a Victron BlueSolar 100v/50a MPPT controller and 530W of panels 2 years ago. They worked fine last year and I haven't payed much attention to the system this season. Last Saturday I noticed my battery voltage was kind of low 12V, even though the monitor said I had a SOC of like 95%. I also saw the charger was on Float charge. I disconnected the panels and opened the controller-battery breaker and then reconnected everything and it went to bulk charge so I walked away fat-dumb-happy. That night I was woken up by a low voltage alarm on my inverter. 10.9V! I shut everything off and dealt with it in the morning. What I found is 2 separate issues. First the SOC is wrong because the monitor auto-synchs incorrectly with a solar charger and this is discussed in the monitor manual. That should not affect the charge controller as the 2 units do not communicate. What I found is the BlueSolar controller is reading a much higher voltage than true. As seen in the attached photo, my correct voltage is 11.8, while the controller is thinking it is 14.4V and only charging at 2.8Amps. I forced it into equalize and it jumped to 25+amps of charge, which it should have been at with 11.8V. I could not find any tech support on Victron's web page. This has been going on for a bit and my batteries are toast from undercharging.
Can you help? How do I fix the Charge controller's erroneous voltage reading? I just bought 3 more expensive batteries and I don't want to toast them too.
Thanks,
Zach
Attached Thumbnails
Click image for larger version

Name:	ChargingData_Small.JPG
Views:	306
Size:	72.3 KB
ID:	156395  
zstine is offline   Reply With Quote
Old 19-09-2017, 17:52   #2
Registered User
 
Simi 60's Avatar

Join Date: Jun 2016
Location: Australia
Boat: Milkraft 60 ex trawler
Posts: 4,653
Re: Did Victron BlueSolar Kill My Batteries?

Might be worth asking the question on the victron blog as well.
I had my issues sorted fast.
Simi 60 is offline   Reply With Quote
Old 19-09-2017, 18:29   #3
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,044
Re: Did Victron BlueSolar Kill My Batteries?

Quote:
Originally Posted by Simi 60 View Post
Might be worth asking the question on the victron blog as well.
I had my issues sorted fast.
Done.. hope CF comes through.
zstine is offline   Reply With Quote
Old 19-09-2017, 19:35   #4
Registered User

Join Date: Aug 2014
Location: Astoria, NY
Boat: Sabre 38
Posts: 566
Did Victron BlueSolar Kill My Batteries?

I have both the solar controllers and monitor. They are a tenth or two different generally, so something is up with yours.

Have you confirmed which reading is correct with a Multimeter?

Maybe the current wires from the controller to batteries are corroded or loose? Can you change out these wires for some new 10 gauge? Anything else between the controller and batteries that could cause resistance / voltage drop (loose busbar, bad lug)?

Victron has great service, so I am sure they can figure out the answer. Would be grateful if you post it here just in case it happens to me!
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Old 19-09-2017, 19:54   #5
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Did Victron BlueSolar Kill My Batteries?

Call Victron directly
Great tech support
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 19-09-2017, 20:02   #6
Registered User
 
zboss's Avatar

Join Date: Sep 2011
Location: On a boat
Boat: 1987 Cabo Rico 38 #117 (sold) & 2008 Manta 42 #124
Posts: 4,174
Re: Did Victron BlueSolar Kill My Batteries?

Are you sure that the 14.4 shown on the iPhone isn’t the absorption charge voltage and the 11.84 the actual battery voltage? If you are using the batteries it will pull down the voltage on the battery, so first try and switch off everything using the batteries. Maybe you have a bad piece of equipment, like a bad fridge compressor or maybe a loose cable that is pulling the voltage down more than it should. The panel is only showing that it’s producing 41 watts so maybe the panel is bad.

Just some ideas.
zboss is offline   Reply With Quote
Old 20-09-2017, 03:53   #7
Registered User

Join Date: Aug 2014
Location: Astoria, NY
Boat: Sabre 38
Posts: 566
Re: Did Victron BlueSolar Kill My Batteries?

Quote:
Originally Posted by zboss View Post
Are you sure that the 14.4 shown on the iPhone isn’t the absorption charge voltage and the 11.84 the actual battery voltage? If you are using the batteries it will pull down the voltage on the battery, so first try and switch off everything using the batteries. Maybe you have a bad piece of equipment, like a bad fridge compressor or maybe a loose cable that is pulling the voltage down more than it should. The panel is only showing that it’s producing 41 watts so maybe the panel is bad.

Just some ideas.

The solar controller has a set absorption voltage of 14.4, which it thinks has been reached, switching itself to absorption mode from bulk.

The batteries are also only accepting 41 watts, which wouldn't be unusual if they were near 100% SOC. But if the monitor is to be believe, they aren't even being charged!

Mystery.
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Old 20-09-2017, 04:54   #8
Registered User
 
Captain Bill's Avatar

Join Date: Apr 2008
Location: Punta Gorda, Fl
Boat: Endeavourcat Sailcat 44
Posts: 3,177
Re: Did Victron BlueSolar Kill My Batteries?

First thing you need to do is get a proper volt meter and determine the real battery voltage measured at the battery posts. Given the low voltage alarm on the inverter it is likely the battery monitor is correct. Then you need to measure the voltage at the output of the solar controller. If it is really at 14.4 then you have a problem with the wiring between the solar controller and the batteries. If the voltage at the posts reads the same as the batteries then you have a controller problem. Remember to measure the voltage on the output posts, not the lug on the cable. The problem may simply be a poor connection as suggested previously.
Captain Bill is online now   Reply With Quote
Old 20-09-2017, 05:00   #9
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Did Victron BlueSolar Kill My Batteries?

How is the system physically wired?
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 20-09-2017, 05:06   #10
Registered User
 
Mike OReilly's Avatar

Join Date: Sep 2011
Location: Good question
Boat: Rafiki 37
Posts: 14,215
Re: Did Victron BlueSolar Kill My Batteries?

I have the same arrangement and also see the voltage within 0.2 v of each other. My solar controller is only one year old though (100/30 version). So far, no problems. Love it!

I too would check things with a good multimeter right at the battery posts, then all along the runs. Something ain’t right...
__________________
Why go fast, when you can go slow.
BLOG: www.helplink.com/CLAFC
Mike OReilly is online now   Reply With Quote
Old 20-09-2017, 05:59   #11
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,044
Re: Did Victron BlueSolar Kill My Batteries?

PO here. Yes, The 11.8 volts was checked with a multi meter and is correct. The controller thinks the batteries have a higher voltage, so I don't see how corroded wires would cause higher voltage, but the wires show no sign of corrosion that I can see.

Main Sail - The system has 6 gauge wire from the batteries to the controller via a 50Amp breaker and the run is less than 3 ft. 10awg to the panel, 20ft run. Controller is stand alone, so that's it.

zboss - Just after the photo I manually put the controller in Equalize mode and I was getting over 300W and 25Amps of charge. So, the controller was limiting the panels to 41 watts, it was not the panel max output.

Contact their Tech support!? I can only find phone numbers for sales on their web page.... I guess I can try that and hope they have a number for Tech Support.

Why would the controller think the battery voltage is HIGHER than the actual true voltage? Corroded wires doesn't make sense.
zstine is offline   Reply With Quote
Old 20-09-2017, 06:08   #12
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Did Victron BlueSolar Kill My Batteries?

Quote:
Originally Posted by zstine View Post
PO here. Yes, The 11.8 volts was checked with a multi meter and is correct. The controller thinks the batteries have a higher voltage, so I don't see how corroded wires would cause higher voltage, but the wires show no sign of corrosion that I can see.

Main Sail - The system has 6 gauge wire from the batteries to the controller via a 50Amp breaker and the run is less than 3 ft. 10awg to the panel, 20ft run. Controller is stand alone, so that's it.

zboss - Just after the photo I manually put the controller in Equalize mode and I was getting over 300W and 25Amps of charge. So, the controller was limiting the panels to 41 watts, it was not the panel max output.

Contact their Tech support!? I can only find phone numbers for sales on their web page.... I guess I can try that and hope they have a number for Tech Support.

Why would the controller think the battery voltage is HIGHER than the actual true voltage? Corroded wires doesn't make sense.
Is it wired to a contiguously wired parallel or series/parallel house bank? Same bank the BMV is monitoring? What are the exact settings for the controller?
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 20-09-2017, 06:19   #13
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,044
Re: Did Victron BlueSolar Kill My Batteries?

The panels are wires in series, two 265W Kyrocera panels. I have 3 Lead Acid batteries in the house bank, the controller connected to directly to the first battery. The monitor shunt is obviously in the Negative Bus, but there is a small ~18awg fused power wire to the monitor, which I guess must also be how it senses voltage(?). That is connected to the 2nd battery in the house bank (Same bank) and there is heavy 0awg wire connecting the 3 house batteries in parallel. The voltage difference should be minimal, certainly not over 2V different.
zstine is offline   Reply With Quote
Old 20-09-2017, 06:45   #14
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Did Victron BlueSolar Kill My Batteries?

Quote:
Originally Posted by fallingeggs View Post
The solar controller has a set absorption voltage of 14.4, which it thinks has been reached, switching itself to absorption mode from bulk.
side note, no controller "switches itself" from CC to CV, that is transition is inherent in the batt chemistry's resistance, even with a simple power supply
john61ct is offline   Reply With Quote
Old 20-09-2017, 07:05   #15
Registered User

Join Date: Aug 2014
Location: Astoria, NY
Boat: Sabre 38
Posts: 566
Re: Did Victron BlueSolar Kill My Batteries?

Quote:
Originally Posted by zstine View Post
The panels are wires in series, two 265W Kyrocera panels. I have 3 Lead Acid batteries in the house bank, the controller connected to directly to the first battery. The monitor shunt is obviously in the Negative Bus, but there is a small ~18awg fused power wire to the monitor, which I guess must also be how it senses voltage(?). That is connected to the 2nd battery in the house bank (Same bank) and there is heavy 0awg wire connecting the 3 house batteries in parallel. The voltage difference should be minimal, certainly not over 2V different.

Where the solar controller is connected might be the problem. Best practice is to connect the positive to battery 1 and the negative to battery 3. Connecting both leads to battery 1 could cause uneven charging.

The monitor, however, is reading the entire bank.

Maybe on an old bank battery 1 could reach 14.4 while the whole bank is lower? Perhaps with already old batteries.

Curious what the Mainesail has to say.
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Victron BlueSolar charge controller mikedefieslife Electrical: Batteries, Generators & Solar 84 14-03-2021 04:46
Victron BlueSolar Charge Controller MPPT 75/115 "Load" Terminal Question PetePetePete Electrical: Batteries, Generators & Solar 5 30-04-2017 03:44
​Victron BlueSolar MPPT as generic DC-DC charger? john61ct Electrical: Batteries, Generators & Solar 6 21-02-2017 21:11
Did I kill my batteries? jr_spyder Electrical: Batteries, Generators & Solar 4 06-07-2014 23:53
Did I Kill It? d design Electrical: Batteries, Generators & Solar 6 11-03-2014 14:27

Advertise Here


All times are GMT -7. The time now is 13:57.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.