DC Negative Grounding to grounding plate - Isolated shaft

Hi there,

In our boat, shaft is isolated from the engine block. We have a very simple electrical system, GPS, VHF, LED lights and basics (bilge pumps etc). There is no AC or we do not use shore power except occasionally charging the batteries in the marinas with extension cable.

All battery negatives goes to the negative bus bar and to the engine. I have a gournding plate a sam copper plate connected to a dynaplate on the hull. (Currently there is nothing connected to it)

As shaft is isolated,
- should I connect the negative bus bar to the ground plate?
Thistle1969 is offline   Reply With Quote
Old 23-09-2015, 08:03   #2
Registered User

Join Date: Mar 2015
Posts: 6
Re: DC Negative Grounding to grounding plate - Isolated shaft

* correction : "square meter copper plate"
Thistle1969 is offline   Reply With Quote
Old 23-09-2015, 08:25   #3
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: DC Negative Grounding to grounding plate - Isolated shaft

Are your thru hulls bonded? If so then I think you need an anode in the water.
Which did not answer your question, but did your boat ever have an HF radio?
I think that may be the reason you have that ground plate, but thru hulls may be even more important to protect than the shaft and prop
a64pilot is offline   Reply With Quote
Old 23-09-2015, 08:30   #4
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: DC Negative Grounding to grounding plate - Isolated shaft

Quote:
Originally Posted by Thistle1969 View Post
...I have a gournding plate a sam copper plate connected to a dynaplate on the hull. (Currently there is nothing connected to it)

As shaft is isolated,
- should I connect the negative bus bar to the ground plate?
Leave it disconnected.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 23-09-2015, 08:57   #5
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: DC Negative Grounding to grounding plate - Isolated shaft

Several considerations:

It the thru hulls are bonded together then she needs a zinc in the system, typically this is on the prop shaft and for this to work shaft must be electrically connected to the thru hulls.

If you care about a propeller then typically need a zinc electrically connected to the prop (shaft zinc again).

If you are concerned about lightning then the mast or mast ground wire should be connected to a ground plate (near the mast base).

Dynaplate is typically for HF radio and don't make great lightning grounds.

If the thru hulls are not bonded then leaving them that way typically works providing that they are high quality bronze and not brass.

I have one bonded ship (IP) and one unbonded (Hunter), both on shore power and neither was taking on water when I last checked.
Frankly is offline   Reply With Quote
Old 23-09-2015, 09:18   #6
Registered User

Join Date: Mar 2015
Posts: 6
Re: DC Negative Grounding to grounding plate - Isolated shaft

There are only two try-hulls under water, both are bronze and seacocks are Marelon. Also they are positioned on opposite sides of the hull. Almost an inch thick hull and corrosion is not concern there.

Shaft has zinc for the propeller.

I am not clear about the answers I've received.

All batteries are connected to the Negative Bus Bar and to the engine. But engine has no electrical connection to the shaft.

- Should I connect negative bus bar to the ground plate to establish connection to the sea?
Thistle1969 is offline   Reply With Quote
Old 23-09-2015, 09:23   #7
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: DC Negative Grounding to grounding plate - Isolated shaft

Quote:
Originally Posted by Thistle1969 View Post
...

Shaft has zinc for the propeller.

I am not clear about the answers I've received.

All batteries are connected to the Negative Bus Bar and to the engine. But engine has no electrical connection to the shaft.

- Should I connect negative bus bar to the ground plate to establish connection to the sea?
Quote:
Originally Posted by Terra Nova View Post
Leave it disconnected.
How can I make this more clear?

Don't...do...anything!
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 23-09-2015, 09:48   #8
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,705
Re: DC Negative Grounding to grounding plate - Isolated shaft

Marine Grounding Systems | West Marine
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 23-09-2015, 10:19   #9
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: DC Negative Grounding to grounding plate - Isolated shaft

Quote:
Originally Posted by Thistle1969 View Post
Hi there,

In our boat, shaft is isolated from the engine block. We have a very simple electrical system, GPS, VHF, LED lights and basics (bilge pumps etc). There is no AC or we do not use shore power except occasionally charging the batteries in the marinas with extension cable.

All battery negatives goes to the negative bus bar and to the engine. I have a gournding plate a sam copper plate connected to a dynaplate on the hull. (Currently there is nothing connected to it)

As shaft is isolated,
- should I connect the negative bus bar to the ground plate?
You should be OK from corrosion standpoint.

Don´t even think about bonding throughulls. That will expose you to stray current corrosion in and around marinas and around other boats.

The question is about lightning. My preference would be to ground the rig to a single metal element in seawater but making sure the rig is isolated from battery negative (check VHF antenna and mast-mounted nav lights). All that said, if the keel is a bolt on keel then why not use the keel?

I confess I did not quite understand the wording about having a Dynaplate and some other plate.
svlamorocha is offline   Reply With Quote
Old 23-09-2015, 21:24   #10
Registered User

Join Date: Mar 2015
Posts: 6
Re: DC Negative Grounding to grounding plate - Isolated shaft

Ah Terra Nova, this is clear. Thanks for the input. So, all negatives are connected to the engine, that's all. My confusion was coming from the idea, if I had to establish connection with seawater or not. Engine remains not bounded to shaft electrically.
Thistle1969 is offline   Reply With Quote
Old 24-09-2015, 08:33   #11
Registered User

Join Date: Oct 2011
Location: Sequim, WA
Boat: Pacific Seacraft Dana 24
Posts: 165
Re: DC Negative Grounding to grounding plate - Isolated shaft

My Cape Dory 31 has all the Spartan bronze sea valves bonded to the lightning ground plate in the keel from the factory. From what I'm reading they shouldn't be! Now I'm confused. Do I disconnect them after 30 years connected or not?
Xthewater is offline   Reply With Quote
Old 24-09-2015, 14:40   #12
Registered User

Join Date: Mar 2014
Location: Anacortes
Boat: previous - Whitby 42 new - Goldenwave 44
Posts: 1,835
Re: DC Negative Grounding to grounding plate - Isolated shaft

The usual setup is bond everything or bond nothing. I.e. don't mix and match.
exMaggieDrum is offline   Reply With Quote
Old 24-09-2015, 14:50   #13
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,483
Re: DC Negative Grounding to grounding plate - Isolated shaft

Quote:
Originally Posted by Xthewater View Post
My Cape Dory 31 has all the Spartan bronze sea valves bonded to the lightning ground plate in the keel from the factory. From what I'm reading they shouldn't be! Now I'm confused. Do I disconnect them after 30 years connected or not?
I'm in the camp that if it has little or minimal corrosion, leave it alone. I lean slightly toward non bonded seacocks myself. But if you have a lightning ground plate, personally I would not connect it to the bonded system.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 24-09-2015, 16:09   #14
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
DC Negative Grounding to grounding plate - Isolated shaft

Curious, do you have some kind of elastomeric damper or something between the transmission and the shaft flange?

Let me clarify why I'm asking and why I asked if your thru hulls were bonded.
I've seen boats with drive savers, which of course electrically isolated the shaft because they didn't use a jumper to keep electrical connectivity, This boat's only Zincs were on the shaft and prop, but it's thru hulls were bonded from the factory, It's thru hull were being de-zincified and had to be replaced as they were no longer connected electrically to a sacrificial anode.
Owner thought they were doing a good thing with the drive saver, but it isolated the zincs from the rest of the underwater metals, all of which were bonded together, now if yours is like there's was a simple jumper wire across the drive saver will restore the bonding of all the underwater metals to the sacrificial anodes.
I'm in the bond everything together and watch your anodes camp, anodes protect everything and just as importantly if you notice them rapidly wasting away, investigate why


Sent from my iPad using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 24-09-2015, 16:39   #15
Registered User

Join Date: May 2012
Posts: 467
Re: DC Negative Grounding to grounding plate - Isolated shaft

This may not apply but after years of replacing zincs only because the diver was there on a bonded boat I became lazy/cheap and stopped having them replaced ! after a about a year a diver stopped by and checked and there was no zinc and the ends of the prop blades were missing at the advice of a some one else in the marina I cut all the bonding and the problem was solved THINGS CHANGE This was in a marina with 200 hundred boats and new neighbors all the time ! just telling you my story not advising!
sartorst is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Testing for isolated alternator? heintje23 Electrical: Batteries, Generators & Solar 6 18-05-2014 10:31
Bobstay Plate / Backing Plate Question zboss Construction, Maintenance & Refit 15 14-08-2013 09:12
Isolated Electrical System ? SabreKai Electrical: Batteries, Generators & Solar 3 09-07-2011 01:55
SSB Whip Antenna Versus Isolated Backstay Camelot Marine Electronics 30 04-12-2010 08:12
Grounding Plate Issue markpj23 Construction, Maintenance & Refit 32 22-02-2008 18:17

Advertise Here


All times are GMT -7. The time now is 21:47.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.