Old 25-09-2015, 09:08   #16
Registered User

Join Date: Sep 2011
Location: Toronto
Boat: Grampian 26
Posts: 101
Re: Dangerous Voltage No Swimming signs at marina

This may answer most questions about electric shock drowning:
__________________

__________________
astokel is offline   Reply With Quote
Old 25-09-2015, 09:18   #17
Registered User

Join Date: Nov 2013
Location: Humble, TX
Boat: Catalina 30/ Sunfish
Posts: 14
Re: Dangerous Voltage No Swimming signs at marina

We recently left our Marina at Clear Lake in TX. The voltage had got so bad that I was changing zincs on our Catalina every 3 months. Some of the problem was from wiring just getting a little old but I think more from so many boats not properly taken care of and literally just sitting there falling apart. The marina did not seem to care so we left. We had about 1.4 volts at the old Marina, our new one only shows about .25-.4 volts. At our old Marina my next door neighbor had a fairly new model Hunter 386. He literally had the blades fall off the propeller one morning. When we inspected the prop you could easily see all the pink spotting that indicates galvanic corrosion in bronze. I have one bronze through hole fitting that was corroding pretty badly after we moved in . When we switched marinas I cleaned it up with a wire brush and some corrosion X and none of the blue corrosion has come back since. I was always kind of amazed at how many boats just sat around at the marina and that people actually must have continued to pay rent there. I have really learned a lesson, I would never move into a Marina again with alot of derilect boats kept there.
__________________

__________________
jlrubin83 is offline   Reply With Quote
Old 25-09-2015, 09:24   #18
Marine Service Provider
 
fstbttms's Avatar

Cruisers Forum Supporter

Join Date: Oct 2006
Location: Under a boat, in a marina, in the San Francisco Bay
Posts: 3,592
Re: Dangerous Voltage No Swimming signs at marina

Quote:
Originally Posted by jlrubin83 View Post
At our old Marina my next door neighbor had a fairly new model Hunter 386. He literally had the blades fall off the propeller on morning. When we inspected the prop you could easily see all the pink spotting that indicates galvanic corrosion in bronze.
You are talking about electrolytic corrosion (also known as stray current corrosion), not galvanic corrosion. Galvanic corrosion is caused by two dissimilar metals being in contact with one another while immersed in an electrolyte. The pink color that you mentioned is caused by dezincification of the metal, where (in the absence of zinc anode protection) the zinc component of the bronze is given up instead, making the metal much more brittle.

__________________
fstbttms is offline   Reply With Quote
Old 25-09-2015, 10:11   #19
Registered User
 
ontherocks83's Avatar

Join Date: Aug 2013
Location: Massachusetts
Boat: Checkmate Strobe 201
Posts: 1,593
Re: Dangerous Voltage No Swimming signs at marina

Quote:
Originally Posted by jlrubin83 View Post
We recently left our Marina at Clear Lake in TX. The voltage had got so bad that I was changing zincs on our Catalina every 3 months. Some of the problem was from wiring just getting a little old but I think more from so many boats not properly taken care of and literally just sitting there falling apart. The marina did not seem to care so we left. We had about 1.4 volts at the old Marina, our new one only shows about .25-.4 volts. At our old Marina my next door neighbor had a fairly new model Hunter 386. He literally had the blades fall off the propeller one morning. When we inspected the prop you could easily see all the pink spotting that indicates galvanic corrosion in bronze. I have one bronze through hole fitting that was corroding pretty badly after we moved in . When we switched marinas I cleaned it up with a wire brush and some corrosion X and none of the blue corrosion has come back since. I was always kind of amazed at how many boats just sat around at the marina and that people actually must have continued to pay rent there. I have really learned a lesson, I would never move into a Marina again with alot of derilect boats kept there.
How do you actually test the water for voltage?
__________________
-Si Vis Pacem Para Bellum
-Molon Labe
ontherocks83 is offline   Reply With Quote
Old 25-09-2015, 10:12   #20
Registered User
 
jreiter190's Avatar

Join Date: Apr 2015
Location: Melbourne, Fl., Patrick Airforce Marina
Boat: 1965 Pearson Alberg 35 #190
Posts: 322
Re: Dangerous Voltage No Swimming signs at marina

This doesn't address the electrified water issue , but, as far as protecting your boat from other boats plugged into the same circuit on the docks goes. When a bunch of boats are on the same circuit, electrically speaking you are all one piece of metal. You want to keep your a.c. ground to protect from shock but you want to break the d.c. loop to isolate your boat from others. Install a galvanic isolator, which is a couple of 50 amp blocking diodes in your A.
C. system . That will solve that part of the problem. Your zincs will thank you. Hope this helps.
__________________
jreiter190 is offline   Reply With Quote
Old 25-09-2015, 11:06   #21
Registered User

Join Date: Nov 2013
Location: Humble, TX
Boat: Catalina 30/ Sunfish
Posts: 14
Re: Dangerous Voltage No Swimming signs at marina

Just take an ohm meter and set it on a low voltage scale. Put the positive end in the water and the ground or black wire to something grounded on your boat.
__________________
jlrubin83 is offline   Reply With Quote
Old 25-09-2015, 11:16   #22
Registered User

Join Date: Feb 2015
Posts: 17
Re: Dangerous Voltage No Swimming signs at marina

If there is submarine cable near by ther could be stray voltage from the nuetral wires that are wrapped around the phase wire .These area the frost to corroad.The minimum voltage would be 7200 volts . Solarsam
__________________
solarsam is offline   Reply With Quote
Old 25-09-2015, 11:26   #23
Registered User
 
ontherocks83's Avatar

Join Date: Aug 2013
Location: Massachusetts
Boat: Checkmate Strobe 201
Posts: 1,593
Re: Dangerous Voltage No Swimming signs at marina

Quote:
Originally Posted by jlrubin83 View Post
Just take an ohm meter and set it on a low voltage scale. Put the positive end in the water and the ground or black wire to something grounded on your boat.
Can you stick the ground end in the ground hole in the a/c outlet on the dock?
__________________
-Si Vis Pacem Para Bellum
-Molon Labe
ontherocks83 is offline   Reply With Quote
Old 25-09-2015, 13:03   #24
Registered User

Join Date: Nov 2013
Location: Humble, TX
Boat: Catalina 30/ Sunfish
Posts: 14
Re: Dangerous Voltage No Swimming signs at marina

There is no need, all the stantions on our boat are grounded. I'm not sure I go putting the ohm meter in an outlet directly
__________________
jlrubin83 is offline   Reply With Quote
Old 28-09-2015, 09:53   #25
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Houston,Tx
Boat: Maxum 37'
Posts: 1,587
Re: Dangerous Voltage No Swimming signs at marina

You want your meter on Volts, NOT ohms.
__________________
capn_billl is offline   Reply With Quote
Old 28-09-2015, 10:05   #26
Registered User

Join Date: Jun 2009
Location: still in a roll of fiberglass around Cape Town
Boat: Leopard 40 (new model)
Posts: 1,201
Re: Dangerous Voltage No Swimming signs at marina

IMHO the most meaningful measurement would be using the AC volts mode of the meter with one of the probes connected to the green safety wire in the dock outlet (or inside the boat, provided there is no iso transformer or galvanic isolator) and the other probe connected to the water via a long wire with some "electrode" at the end ( I use a copper pipe). As you move the electrode you may see a change in reading that tells you which way the gradient goes.


Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
__________________
svlamorocha is offline   Reply With Quote
Old 28-09-2015, 10:27   #27
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Houston,Tx
Boat: Maxum 37'
Posts: 1,587
Re: Dangerous Voltage No Swimming signs at marina

I agree, the one reading I'm most concerned about is the prop shaft vs water voltage. The zincs should be connected to the boats DC grounding system, and at the same voltage.
__________________
capn_billl is offline   Reply With Quote
Old 28-09-2015, 13:17   #28
Registered User

Join Date: Jun 2009
Location: still in a roll of fiberglass around Cape Town
Boat: Leopard 40 (new model)
Posts: 1,201
Re: Dangerous Voltage No Swimming signs at marina

Quote:
Originally Posted by capn_billl View Post
I agree, the one reading I'm most concerned about is the prop shaft vs water voltage. The zincs should be connected to the boats DC grounding system, and at the same voltage.
The prop shaft is in the water, hence at same potential as water near the boat. That does not eliminate the danger caused by water at potential different than earth in places close to AC leaks into water.

This is because a boat with a proper installation will have chassis of appliances, etc connected to the non-current carrying (hence zero drop) green wire that takes potential from a ground rod somewhere. If the water is at a different potential than the green wire then there is unnecessary risk.

I trust this explains why the relevant measure to detect AC leaks into water is delta voltage between water and green wire/ground rod.

The ABYC electric shock drowning guru has a good video on this.





Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
__________________
svlamorocha is offline   Reply With Quote
Old 28-09-2015, 13:24   #29
Registered User

Join Date: Jun 2009
Location: still in a roll of fiberglass around Cape Town
Boat: Leopard 40 (new model)
Posts: 1,201
Re: Dangerous Voltage No Swimming signs at marina

Quote:
Originally Posted by jlrubin83 View Post
There is no need, all the stantions on our boat are grounded. I'm not sure I go putting the ohm meter in an outlet directly
They are "grounded" but not necessarily to the potential you want, which is earth as in a ground rod next to the transformer. There has been plenty of science and engineering (and death statistics) used in the development of electrical safety best practices.

On a related matter, you should not use an ohm meter for this. You want a voltage meter. An ohm meter will get fried by AC.
__________________

__________________
svlamorocha is offline   Reply With Quote
Reply

Tags
danger

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Marina Ixtapa dangerous swell warning. Muckle Flugga Marinas 1 06-08-2015 08:28
Low voltage vs higer voltage solar Singleprop Electrical: Batteries, Generators & Solar 11 06-07-2015 20:35
President Bush signs SAFE port act ... sort of GordMay Off Topic Forum 1 13-12-2006 05:55
Gov. Bush signs law rleslie Cruising News & Events 5 31-10-2006 12:27



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 08:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.