Changing AC from 100v 50hz to 120v 60hz

Howdy folks -

I need a wee bit of adult supervision!

I'm looking at a boat with a 100v 50hz AC system. I would like to replace that with a 110/120v 60hz system. Excluding the 50hz dependent appliances, what will I have to replace in addition to the inverter/charger?

Would the shore power system be effected by this change?

Much mahalo for any knowledge or experience you can share!

B.
Bodega Bob is offline   Reply With Quote
Old 23-07-2017, 13:11   #2
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Changing AC from 100v 50hz to 120v 60hz

You MAY need to replace wires with heftier wires. In order to know if this will be necessary you need to look at the markings in the wires that go a) from the panel to the water heater b) from the panel to outlets and other loads and c) from shorepower inlet to the panel. You are looking for labels that say "2.5", "4", "6", etc square milimeters. If you can specify that boat make and model we can be more specific.
svlamorocha is offline   Reply With Quote
Old 23-07-2017, 13:12   #3
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Changing AC from 100v 50hz to 120v 60hz

You will have to replace the AC element of the water heater, but do not do that without checking that the wire gauge is sufficient.
svlamorocha is offline   Reply With Quote
Old 23-07-2017, 13:51   #4
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Changing AC from 100v 50hz to 120v 60hz

It takes a larger wire to deliver the same power at lower voltage, so your 100v wiring should be the same size as 120v (or perhaps a little large). So there should be no problem with wire size. Check that the breakers are rated for 120v 60hz.
__________________
Paul
Paul L is offline   Reply With Quote
Old 23-07-2017, 14:32   #5
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Changing AC from 100v 50hz to 120v 60hz

I assumed you meant to say 240V aka 220V instead of 100V.
svlamorocha is offline   Reply With Quote
Old 23-07-2017, 15:17   #6
Registered User

Join Date: Jul 2017
Boat: CSY 44 Pilothouse Ketch
Posts: 11
Re: Changing AC from 100v 50hz to 120v 60hz

svlamorocha - 100v 50hz. Thx for the tip on the water heater.

Paul L. THX for the wire gauge clarification.

Can you clarify the effect on the breakers in the distribution panel? They care only about amperage, correct?

Amp = volt x watt. A 30 amp fuse trips @ 30 amps no matter what combination of voltage & wattage produces it?

Any insight on the effect this change would have on the existing shore power set up? Are there any bits that would need to be changed in that system?

Much mahalo for the help!
B.
Bodega Bob is offline   Reply With Quote
Old 23-07-2017, 15:24   #7
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by Bodega Bob View Post
svlamorocha - 100v 50hz.
What sort of boat came with a 100V 50Hz electrical system?
svlamorocha is offline   Reply With Quote
Old 23-07-2017, 15:25   #8
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Changing AC from 100v 50hz to 120v 60hz

I've never heard of 100V 50 hz, where is that the standard?
a64pilot is offline   Reply With Quote
Old 23-07-2017, 17:54   #9
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by a64pilot View Post
I've never heard of 100V 50 hz, where is that the standard?
Japan
__________________
Paul
Paul L is offline   Reply With Quote
Old 24-07-2017, 21:02   #10
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by Bodega Bob View Post
Howdy folks -

I need a wee bit of adult supervision!

I'm looking at a boat with a 100v 50hz AC system. I would like to replace that with a 110/120v 60hz system. Excluding the 50hz dependent appliances, what will I have to replace in addition to the inverter/charger?

Would the shore power system be effected by this change?

Much mahalo for any knowledge or experience you can share!

B.
You should not have to change anything except the 50hz appliances and the shore power inlet.
mitiempo is offline   Reply With Quote
Old 25-07-2017, 00:16   #11
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by mitiempo View Post
You should not have to change anything except the 50hz appliances and the shore power inlet.
These days, most appliances are made multi frequency (50 & 60Hz) at the factory if also exported.

It is cheaper for them to standardise parts.

However they are labeled and advertised with the local frequency so that national distributers can get the local safety certificates cheaper and easier.

Test them first, before replacing.
You may not have any problem
Pelagic is offline   Reply With Quote
Old 25-07-2017, 05:09   #12
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,436
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by Bodega Bob View Post
.....

Amp = volt x watt. ......
Small correction; Amp = watt/volt
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 25-07-2017, 11:57   #13
Registered User

Join Date: Sep 2013
Location: Alert Bay, Vancouver Island
Boat: 35ft classic ketch/yawl.
Posts: 1,984
Images: 4
Send a message via Skype™ to roland stockham
Re: Changing AC from 100v 50hz to 120v 60hz

Depending on what appliances you have it can be easier to fit a 220v inverter rather than change equipment. Also improves isolation from shore power. I run all 'mains services' from the onboard inverter. The battery charger is the only item connected to shore power. Effectively the same as using an isolation transformer but lighter and cheaper. If you also need 120v add a second inverter
roland stockham is offline   Reply With Quote
Old 25-07-2017, 21:34   #14
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by roland stockham View Post
Depending on what appliances you have it can be easier to fit a 220v inverter rather than change equipment. Also improves isolation from shore power. I run all 'mains services' from the onboard inverter. The battery charger is the only item connected to shore power. Effectively the same as using an isolation transformer but lighter and cheaper. If you also need 120v add a second inverter
Why would the op need a 220v inverter when the original voltage is 100?

It is close enough to North American voltage to not be an issue.
mitiempo is offline   Reply With Quote
Old 25-07-2017, 22:04   #15
Registered User

Join Date: Sep 2013
Location: Alert Bay, Vancouver Island
Boat: 35ft classic ketch/yawl.
Posts: 1,984
Images: 4
Send a message via Skype™ to roland stockham
Re: Changing AC from 100v 50hz to 120v 60hz

Quote:
Originally Posted by mitiempo View Post
Why would the op need a 220v inverter when the original voltage is 100?

It is close enough to North American voltage to not be an issue.
Because the 100v is a typo, there is no such thing as 100v AC, never heard of 100v dc systems either. It is either 120v for N American standard or 240v for European.
It is possible the op has measured the actual voltage coming out of the dock receptical on a pontoon and found it to be 100v which is not uncommon but it is still nominally 120v. (also a reason I prefer my own inverter as a power source!!)
roland stockham is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
220v/50hz to 110v/60hz - Looking for Options Kaptain Ken Electrical: Batteries, Generators & Solar 24 20-06-2017 05:24
US Microwave on 120v 50Hz SV Enough Propellers & Drive Systems 2 01-02-2017 01:10
Connecting 50hz Italian boat to 60hz US power Inthefridge Electrical: Batteries, Generators & Solar 20 09-12-2016 10:59
European power 50hz 60hz solution tulsag Electrical: Batteries, Generators & Solar 0 28-10-2014 07:11
getting 220v 60hz and 110v 60hz at same time Overlord Marine Electronics 9 17-05-2012 14:51

Advertise Here


All times are GMT -7. The time now is 03:43.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.