Old 27-11-2018, 20:22   #1
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,184
Images: 6
Cant get Nothern Lights Generator to start

So far i have been following the bleeding procedure and I got the fuel to show up at the inlet of Injection pump. Manual states that if engine does not start after typical bleeding procedure, you crack the injectors, and use primer lever to get fuel to each injector line one at the time.

Well I cant get the fuel to come out of injector line nuts. Ive been pumping for a while. I also tried cranking with injector nuts loose.

This generator has been sitting for 2 years. I did personally witness it starting when i went to look at the boat prior to purchase. It was somewhat winterized 2 years ago. Namely only RV antifreeze was pumped through the raw water side. But oil and fuel filters have not been changed.

I am not very familiar with these and any experience or advice would be appreciated.
phorvati is online now   Reply With Quote
Old 28-11-2018, 00:28   #2
Registered User

Join Date: Dec 2009
Location: Australia
Boat: BUILT!!! Roberts Mauritius 43ft
Posts: 3,659
Re: Cant get Nothern Lights Generator to start

Maybe something here?


https://citimarinestore.com/citiguid...hooting-guide/






Clive
coopec43 is online now   Reply With Quote
Old 28-11-2018, 04:36   #3
Registered User
 
MartinR's Avatar

Join Date: Feb 2015
Location: Sweden
Boat: 73´ULDB custom ketch
Posts: 1,069
Re: Cant get Nothern Lights Generator to start

You can always try to release the injectors a little and then crank the engine. When fuel appears at the injectors, continue cranking and tighten them.
MartinR is offline   Reply With Quote
Old 28-11-2018, 04:58   #4
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,333
Re: Cant get Nothern Lights Generator to start

If you can get fuel out of the high pressure lines by rotating the engine with the starter motor, tighten the nuts and use the preheat/ glowplug position on the keyswitch. The preheat is very important. Also wise to temporarily close the raw water intake to avoid backflooding the exhaust while cranking a reluctant engine.
If all fails and no fuel is seen at the injectors, it might mean that the injector pump is stuck in the no fuel position and this can be checked by unscrewing the stop solenoid at the rear of the pump housing and seeing if the pump control rack moves or not. If you're not confident doing this , probably best to get a mechanic.
Finally... check the stop solenoid operation .... it is activated to run and with no power the engine will not run.
skipperpete is offline   Reply With Quote
Old 28-11-2018, 07:04   #5
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,184
Images: 6
Re: Cant get Nothern Lights Generator to start

Quote:
Originally Posted by skipperpete View Post
If you can get fuel out of the high pressure lines by rotating the engine with the starter motor, tighten the nuts and use the preheat/ glowplug position on the keyswitch. The preheat is very important. Also wise to temporarily close the raw water intake to avoid backflooding the exhaust while cranking a reluctant engine.
If all fails and no fuel is seen at the injectors, it might mean that the injector pump is stuck in the no fuel position and this can be checked by unscrewing the stop solenoid at the rear of the pump housing and seeing if the pump control rack moves or not. If you're not confident doing this , probably best to get a mechanic.
Finally... check the stop solenoid operation .... it is activated to run and with no power the engine will not run.
Raw water is closed. In fact rv antifreeze has been in there for 2 years. Step 1 is getting fuel to injectors. I am not going to check the preheat until I get fuel where it needs to be.
So if stop solenoid is not energized (activated), I wont see fuel at the injector lines. That seems like a legitimate reason why there's no fuel, even when I'm cranking.
What does not make sense then is manual saying you can use prime lever to get fuel all the way to injectors. It does not mention having to activate stop solenoid while pruming.

If solenoid indeed is blocking the fuel until energized, then its continuous duty, Meaning you have to keep solenoid energized in order to allow fuel to flow and generator to run. Continuous duty solenoids are $$$. I would be surprised of that's the case.

I'll check the injection pump rack to see if it's stuck.
phorvati is online now   Reply With Quote
Old 28-11-2018, 07:43   #6
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,184
Images: 6
Re: Cant get Nothern Lights Generator to start

I'm really reading the damn manual again. I was not holding the bypass/preheat while cranking. So bypass bypasses the stop solenoid during cranking. And I guess the solenoid must be continuous duty.
phorvati is online now   Reply With Quote
Old 28-11-2018, 08:30   #7
Registered User

Join Date: Feb 2010
Location: US
Posts: 219
Re: Cant get Nothern Lights Generator to start

We had been having trouble and it was usually fuel drain back from the unit due to some air leak somewhere. Replaced hoses and valves which may have helped. But an electric fuel pump replacement from the auto store got it started again.
Locquatious is offline   Reply With Quote
Old 28-11-2018, 08:35   #8
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Cant get Nothern Lights Generator to start

Most all gensets during starting bypass the low oil PSI Murphy switch because if they didn’t then of course they wouldn’t start cause no oil pressure would be sensed.

I’d be surprised if your stop solenoid were continuous duty myself, usually they are not and if they fail, it just means you can’t turn the thing off, then you have to move the lever manually.

on edit, most low oil PSI switches are normally open and close when there is pressure, these are easily bypassed by merely jumping the switch.
a64pilot is offline   Reply With Quote
Old 28-11-2018, 08:42   #9
Registered User

Join Date: Sep 2015
Location: East Coast Florida
Boat: Chris Craft 38 Commander 1965
Posts: 482
Re: Cant get Nothern Lights Generator to start

Many diesels have continuous duty solenoids. When you press the start button you should hear/feel the solenoid click. Or just apply a 12v jumper to it's positive input terminal to check it directly without the start switch.
Squanderbucks is offline   Reply With Quote
Old 28-11-2018, 09:45   #10
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,333
Re: Cant get Nothern Lights Generator to start

What model NL genset are we trying to start, I had assumed it was in the 5-15 kva group with the Shibaura engine but if it's in the heavy duty series with John Deere engines my comments will not apply.
skipperpete is offline   Reply With Quote
Old 28-11-2018, 11:27   #11
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: Cant get Nothern Lights Generator to start

The engine won’t start without the bypass switch held on, and continued held on for maybe 5 seconds after it starts.

And when bleeding the injectors, I’m pretty sure you need to hold the bypass switch on again, otherwise the stop solenoid will block fuel flow. It’s an energize to run solenoid.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 29-11-2018, 16:25   #12
Registered User

Join Date: May 2008
Location: mexico
Boat: 75' steel sutton ketch,Warwick 70' aluminum sloop
Posts: 127
Re: Cant get Nothern Lights Generator to start

the fuel rack stuck on mine,,,,,,,,, after sitting for a number of years
s/v michaela is offline   Reply With Quote
Old 29-11-2018, 17:09   #13
Registered User

Join Date: Jul 2016
Posts: 238
Re: Cant get Nothern Lights Generator to start

the cutoff is continuous duty...
easy to get and replace..
while cranking is yours getting 12v? if not..check the control box
relays..or jumper 12v directly to it...
open the injector lines and crank..stop when fuel comes out..
close them..crank again..it should start...DON'T FORGET TO OPEN
the RAW WATER WHEN IT STARTS!!! you destroy the raw water impeller
in seconds...been there done that...oops


-dkenny64
dkenny64 is offline   Reply With Quote
Old 29-11-2018, 18:20   #14
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,184
Images: 6
Re: Cant get Nothern Lights Generator to start

M643 older version. So I looked over the wiring diagram and can confirm that it has continuous duty stop solenoid. So I just need to press the preheat/bypass before cranking if I expect to have fuel pass injection pump. In fact, preheat engages run relay and then even if you let go of preheat, run relay is still engaged so fuel rack is engaged until I press the shut down. Fancy stuff they put in to make the unit more apealing. And I think safer, because if stop solenoid fails, unit dies...no need to manually shift the lever or jamb towels in the air intake. I am just glad they shared the wiring diagram.Click image for larger version

Name:	Screenshot_2018-11-29-21-20-08.jpeg
Views:	525
Size:	61.9 KB
ID:	181481
phorvati is online now   Reply With Quote
Old 29-11-2018, 18:23   #15
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,184
Images: 6
Re: Cant get Nothern Lights Generator to start

Quote:
Originally Posted by phorvati View Post
M643 older version. So I looked over the wiring diagram and can confirm that it has continuous duty stop solenoid. So I just need to press the preheat/bypass before cranking if I expect to have fuel pass injection pump. In fact, preheat engages run relay and then even if you let go of preheat, run relay is still engaged so fuel rack is engaged until I press the shut down. Fancy stuff they put in to make the unit more apealing. And I think safer, because if stop solenoid fails, unit dies...no need to manually shift the lever or jamb towels in the air intake. I am just glad they shared the wiring diagram.Attachment 181481
I've had a faulty solenoid on my main diesel engine recently so I am very cautious.
phorvati is online now   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Crew Available: Trying to Gain More Experience. MD Nothern VA AmirB Crew Positions: Wanted & Available 0 24-06-2017 09:00
breaker problem on Nothern Light 30kw generator 85 Superstar Electrical: Batteries, Generators & Solar 0 17-01-2013 08:50
My alternator is tested but I cant get it to work . Am I going blind ? flemmingsveen Electrical: Batteries, Generators & Solar 15 21-02-2012 10:33
Nothern Light Generator question..... gbanker Electrical: Batteries, Generators & Solar 10 21-03-2011 17:13
U.S. Navy Increasing Presence - Nothern Indian Ocean and Gulf of Aden DennisNAlison Cruising News & Events 9 13-01-2010 20:14

Advertise Here


All times are GMT -7. The time now is 06:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.