Re: Burned ground wire on inverter

Well this is somewhat timely. I just checked my brand new Renogy 2000 Watt inverter, still sitting on the work bench, and there is continuity internally between the AC ground and DC negative.
toddster8 is offline   Reply With Quote
Old 31-07-2019, 09:34   #32
Registered User

Join Date: Jun 2016
Posts: 850
Re: Burned ground wire on inverter

Quote:
Originally Posted by sailorchic34 View Post
I will note that I agree with TransmitterDan and I feel that connecting the AC ground to the boats DC ground can create problems. ABYC is a good code, but it assumes everything will always be perfect. On a boat that is almost never the case. So I do not have AC and DC ground connected on my boat. But that's just me.
So what I'm hearing is that if we are connected to shore power, the AC and DC ground should be connected, but if on inveter then no?
sailingunity is offline   Reply With Quote
Old 31-07-2019, 09:40   #33
Registered User

Join Date: Dec 2016
Location: PNW
Boat: J/42
Posts: 938
Re: Burned ground wire on inverter

There are enough poles on the (manual) transfer switch to disconnect the inverter ground whenever shore power is on. Seems easy. I wonder how this works in the more expensive charger/inverters with automatic transfer?
toddster8 is offline   Reply With Quote
Old 31-07-2019, 09:42   #34
Registered User

Join Date: Jun 2016
Posts: 850
Re: Burned ground wire on inverter

I better call Victron and see what they say.
sailingunity is offline   Reply With Quote
Old 31-07-2019, 09:44   #35
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Burned ground wire on inverter

Quote:
Originally Posted by sailingunity View Post
So what I'm hearing is that if we are connected to shore power, the AC and DC ground should be connected, but if on inveter then no?

I would say never run the inverter if your on shore power. But if you must, say with a 220v EU boat in a US marine, either install a much larger ground wire from inverter to ground or, disconnect the ground wire to the inverter. Pretty sure your getting some harmonic imbalance between shore power phase and inverter.


I will note that back in 1990 we did install larger ground wires in PC data centers. That does "solve" the issue, sort of. I think the newer NEC addresses this. But it's been a while since I read it.
sailorchic34 is offline   Reply With Quote
Old 31-07-2019, 09:46   #36
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Burned ground wire on inverter

Quote:
Originally Posted by GordMay View Post
Indeed.
Which the transfer switch (should) accomplish.


What transfer switch?
I believe we are confusing neutral again, my Inverter has an option of bonding the neutral with the ground I believe when the inverter is functioning.

Besides I’m unaware of specific “Marine” inverters, my Magnum MS 2812 for instance is very often used for house solar installations, so is it a “Marine” inverter? Is my Outback 80 a Marine solar controller? I know my Canadian Solar panels are not Marine solar panels.

I guess my point is that often the title Marine is misrepresented to dictate a higher price, like Marine batteries, I don’t think my Lifeline batteries are Marine either.

So the name marine doesn’t necessarily mean anything. West Marine is full of Marine batteries and other not necessarily quality products with Marine in the title.

See attached screen shot, read where it says ensuring a safe ground

I am not, nor do I pretend to be a Marine electrician, I was licensed for residential work, but a boat is a whole different thing than a house.
Click image for larger version

Name:	IMG_0052.jpg
Views:	136
Size:	198.9 KB
ID:	196965
Click image for larger version

Name:	IMG_0053.jpg
Views:	293
Size:	209.6 KB
ID:	196966
a64pilot is offline   Reply With Quote
Old 31-07-2019, 09:47   #37
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Burned ground wire on inverter

Quote:
Originally Posted by toddster8 View Post
Well this is somewhat timely. I just checked my brand new Renogy 2000 Watt inverter, still sitting on the work bench, and there is continuity internally between the AC ground and DC negative.

That would be correct. But check if either hot leg on inverter output has continuity to dc negative. THAT is the issue.
sailorchic34 is offline   Reply With Quote
Old 31-07-2019, 10:41   #38
Registered User
 
wingless's Avatar

Join Date: Aug 2013
Location: Florida
Boat: 2000 Searay 380 Sundancer
Posts: 1,087
Re: Burned ground wire on inverter

The OEM wiring on my 2000 380DA Sea Ray, w/ factory shore power and factory generator has been working fine.

They use a galvanic isolator between the green ground wire on each 30A shore power inlet and the boat's green ground system. All of the green ground wires on the boat are connected to this system.

My boat has a Guest Dynaplate sintered bronze bonding plate attached to the hull exterior, connected to the green bonding wires.

On my boat, both engines have a large ground stud. On each stud I have thick black battery negative wires and thick green bonding wires. These are the only locations where battery negative and green bonding wires are connected together.

My small inverter is used for additional receptacles, for television power and for convenience outlets around the boat, used for phone and laptop chargers. The original AC receptacles remain wired to the main circuit panel, powered by shore power or generator power.
__________________
2000 SeaRay 380 Sundancer Mercruiser
454 MAG MPI Horizon 380hp / Westerbeke 7.0KW BCGB
many cool mods
wingless is offline   Reply With Quote
Old 31-07-2019, 11:50   #39
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Burned ground wire on inverter

Your saying your shorepower ground is connected to your external plate in the water?
You sure? Maybe they just used green wire to ground the boats metals?
a64pilot is offline   Reply With Quote
Old 31-07-2019, 11:55   #40
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,101
Re: Burned ground wire on inverter

Quote:
Originally Posted by a64pilot View Post
What transfer switch?
I believe we are confusing neutral again, my Inverter has an option of bonding the neutral with the ground I believe when the inverter is functioning.

Besides I’m unaware of specific “Marine” inverters, my Magnum MS 2812 for instance is very often used for house solar installations, so is it a “Marine” inverter? Is my Outback 80 a Marine solar controller? I know my Canadian Solar panels are not Marine solar panels.

I guess my point is that often the title Marine is misrepresented to dictate a higher price, like Marine batteries, I don’t think my Lifeline batteries are Marine either.

So the name marine doesn’t necessarily mean anything. West Marine is full of Marine batteries and other not necessarily quality products with Marine in the title.

See attached screen shot, read where it says ensuring a safe ground

I am not, nor do I pretend to be a Marine electrician, I was licensed for residential work, but a boat is a whole different thing than a house.
Attachment 196965
Attachment 196966
Marine inverters are different and ABYC requires they meet UL and SAE standards not required of non-marine units. None of the non-marine units has the auto neutral switching.

PM me an email address and I'll send you a copy of the standard.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is online now   Reply With Quote
Old 31-07-2019, 12:02   #41
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Burned ground wire on inverter

I understand the requirements, but just as a reference the Magnum meets those standards, and isn’t to my knowledge advertised as a “marine” inverter, but it may be.
But I bet I can find Marine labeled inverters that don’t meet the ABYC standards, which if I understand correctly aren’t requirements, but are a standard, and often a good idea.
I guess I’m saying that you need to either educate yourself or hire a Marine electrician, and not go by labels.
a64pilot is offline   Reply With Quote
Old 31-07-2019, 12:22   #42
Registered User
 
wingless's Avatar

Join Date: Aug 2013
Location: Florida
Boat: 2000 Searay 380 Sundancer
Posts: 1,087
Re: Burned ground wire on inverter

Quote:
Originally Posted by wingless View Post
They use a galvanic isolator between the green ground wire on each 30A shore power inlet and the boat's green ground system. All of the green ground wires on the boat are connected to this system.

My boat has a Guest Dynaplate sintered bronze bonding plate attached to the hull exterior, connected to the green bonding wires.

On my boat, both engines have a large ground stud. On each stud I have thick black battery negative wires and thick green bonding wires. These are the only locations where battery negative and green bonding wires are connected together.
Quote:
Originally Posted by a64pilot View Post
Your saying your shorepower ground is connected to your external plate in the water?
You sure? Maybe they just used green wire to ground the boats metals?
Yes, you are correct. My error, sorry for creating confusion.

Different green wires. One for shore power Earth ground, receptacle to galvanic isolator, then to boat AC wiring. Separate green wire for underwater metal bonding, to hull zinc and to sintered bronze hull plate.

One of those is connected to battery negative on each of the engine blocks.
__________________
2000 SeaRay 380 Sundancer Mercruiser
454 MAG MPI Horizon 380hp / Westerbeke 7.0KW BCGB
many cool mods
wingless is offline   Reply With Quote
Old 31-07-2019, 13:20   #43
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Burned ground wire on inverter

It sure seems as if Magnum promotes their products as designed for the marine market segment.

https://www.magnum-dimensions.com/si...glepgs-web.pdf
transmitterdan is offline   Reply With Quote
Old 31-07-2019, 22:48   #44
Registered User

Join Date: Sep 2013
Location: Alert Bay, Vancouver Island
Boat: 35ft classic ketch/yawl.
Posts: 1,981
Images: 4
Send a message via Skype™ to roland stockham
Re: Burned ground wire on inverter

Quote:
Originally Posted by boatpoker View Post
The DC negative and AC ground should always be bonded on the vessel
(as per ABYC).

I believe you may be thinking of the AC ground and AC neutral which should only be bonded at the power source whether generator, inverter or shore power.

I have never understood why ABYC do this. European regs say the opposite that AC ground should be connected to seawater and DC ground seperate and left floating. The issue with connecting grounds is that it is often don by connecting both grounds to a seacock bolt or similar. If the connection comes adrift leaving AC and DC connected to each other but no to seawater then every case and all DC equipment will potentialy at hot wire volts.
roland stockham is offline   Reply With Quote
Old 31-07-2019, 22:54   #45
Registered User

Join Date: Sep 2013
Location: Alert Bay, Vancouver Island
Boat: 35ft classic ketch/yawl.
Posts: 1,981
Images: 4
Send a message via Skype™ to roland stockham
Re: Burned ground wire on inverter

I am wondering if you have a working RCD. It should have tripped if you have a significant current flowing to earth. If the RCD is fitted and working my guess would be a loose connection on the DC+ cause a short to the casing nd then earth until the ground wire acted as a fuse. In that case where is the main batt fuse and why did it not blow? Sound like you need to check the earths and fussing/RCD's
roland stockham is offline   Reply With Quote
Reply

Tags
inverter

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Negative Ground vs Positive Ground History Question. Wotname Electrical: Batteries, Generators & Solar 23 26-04-2021 04:22
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
9 V difference between ground and ground Arrandir Electrical: Batteries, Generators & Solar 12 19-07-2018 22:51
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
Smoking Hot Ground Wire Zydeco Electrical: Batteries, Generators & Solar 9 15-02-2011 04:52

Advertise Here


All times are GMT -7. The time now is 13:08.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.