ANL Fuse/holder getting real hot

Hello everyone, I have a fuse holder that allegedly handles 750A but I can hardly reach 400A for a few minutes before it gets cray hot. Temperature increases around as well of course. 95mm2 cable on the left, copper bar to the right. Right now the fuse is a 425A, maybe not a true ANL ? Any ideas ?Click image for larger version

Name:	20190114_211455.jpg
Views:	426
Size:	426.0 KB
ID:	183815
Also, is there a way to tell what should be the max. 230VAC amperage (fuse) if I decide that 400A is the max 12VDC ? (let's pretend the inverters work at 90% efficiency)
rom is offline   Reply With Quote
Old 14-01-2019, 12:42   #2
Registered User

Join Date: Jun 2010
Location: Easton, MD
Boat: 15' Catboat, Bristol 35.5
Posts: 3,510
Re: ANL Fuse/holder getting real hot

The amperage a fuse opens at is not a function of voltage but they are rated at a max volage.
kmacdonald is offline   Reply With Quote
Old 14-01-2019, 12:55   #3
Registered User
 
ThereAndBack's Avatar

Join Date: Jun 2018
Boat: Voyage 430
Posts: 401
Re: ANL Fuse/holder getting real hot

Look for a loose connection, extra washers where there shouldn't be any, bad crimps, etc. Anything causing impedance may be heating up. Take the fuse out and look for corrosion. Etc.
ThereAndBack is offline   Reply With Quote
Old 15-01-2019, 00:32   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,634
Re: ANL Fuse/holder getting real hot

Are your washers between connections? There was just a post on this. A bad cable crimp could also do it.

I don't understand 2nd q. The inverter manual should provide the dc and ac fusing to use and cable sizes.
smac999 is offline   Reply With Quote
Old 15-01-2019, 02:41   #5
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,082
Images: 241
Re: ANL Fuse/holder getting real hot

Quote:
Originally Posted by rom View Post
... 95mm2 cable on the left, copper bar to the right. Right now the fuse is a 425A, maybe not a true ANL ? Any ideas ...
A 95 mm2 Cu cable is only rated about 292A free air, or 250A bundled.
A 185 mm2 Cu cable is rated just over 400A
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 15-01-2019, 03:05   #6
Registered User

Join Date: Aug 2016
Location: ABC's
Boat: Prout Snowgoose 35
Posts: 1,756
Re: ANL Fuse/holder getting real hot

Quote:
Originally Posted by GordMay View Post
A 95 mm2 Cu cable is only rated about 292A free air, or 250A bundled.
A 185 mm2 Cu cable is rated just over 400A
The BlueSeaSystems app seems to think that a 2m 95mm2 conductor terminated on a fuse should be fine handling 412a

That's all well and good but the OP is stating that it's the fuse getting how not the cable.
mikedefieslife is offline   Reply With Quote
Old 15-01-2019, 03:59   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,082
Images: 241
Re: ANL Fuse/holder getting real hot

There can be large differences between ampacity data/ratings from different sources.
Metric values are taken from ISO/FDIS 10133.
The following plot compares five standards. These curves show that AC ratings tend to be lower than DC ratings (e.g. NEC versus ABYC).
For DC applications, the JASO (Japan) and ABYC (US) ratings are similar, and the ISO (EU & Brit') ratings are about 15% lower (than ABYC).

I prefer the more conservative rating.





__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 15-01-2019, 04:00   #8
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 736
Re: ANL Fuse/holder getting real hot

Quote:
Originally Posted by mikedefieslife View Post
The BlueSeaSystems app seems to think that a 2m 95mm2 conductor terminated on a fuse should be fine handling 412a

That's all well and good but the OP is stating that it's the fuse getting how not the cable.
Yes Mike and I think that is for a 105°C rated cable. GordMay is also right if he is talking about 60°C or maybe 70°C cables.

Anyway, the problem is the ANL fuse and/or fuse holder. The shunt on the negative side remains rather cold in that 400A test of mine. Of course washers are on the good side and both the fuse and the holder are like new and clean.

As for the question about conversion to 230VAC. I now have 2 victron multiplus 3000 in parallel that are capable of killing my batteries or worse set the DC cables on fire.
First I need a proper DC fuse, at this stage it seems 350A seems to be the max because of that ANL problem.
Second, 230VAC output of the multis go into a 30mA breaker currently rated 40A. That is way too much, as it is the DC fuse that will trip should I use the electric oven, coffe machine, and water heater at the same time...
So what I want is a 230VAC breaker to be as high as possible, yet it should trip before the DC fuse. If I am limiting 230VAC with a 16A breaker, the system may then use up to 340A from the batteries. 16A x 230V = 3680 / 0.9 (efficiency) = 4088 A / 12V = 340 A. But I don't think that formula is correct, that was my question.
rom is offline   Reply With Quote
Old 15-01-2019, 09:18   #9
Registered User

Join Date: Mar 2015
Location: Boston's North Shore
Boat: Pearson 10M
Posts: 839
Re: ANL Fuse/holder getting real hot

power (Watts) =Voltage * Amps
Volts = Resistance * current (Amps)

As you work through your electrical calculations, try to use the correct units. It will give you more confidence in your results and will help others interpret your questions.
guyrj33 is offline   Reply With Quote
Old 15-01-2019, 09:28   #10
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 361
Re: ANL Fuse/holder getting real hot

There should be no washers between the fuse holder and cable lugs. I can see a 425A rated fuse get warm to hot when reaching 400 amps. I would try a new fuse.
Zil is offline   Reply With Quote
Old 15-01-2019, 09:32   #11
Registered User

Join Date: Jun 2010
Location: Easton, MD
Boat: 15' Catboat, Bristol 35.5
Posts: 3,510
Re: ANL Fuse/holder getting real hot

It's normal for fuses to get hot at amperages close to their rating. They melt open at their rated amperage and their temp increases in proportion to current.
kmacdonald is offline   Reply With Quote
Old 15-01-2019, 09:43   #12
Registered User

Join Date: Oct 2014
Posts: 7,310
Re: ANL Fuse/holder getting real hot

Quote:
Originally Posted by GordMay View Post
A 95 mm2 Cu cable is only rated about 292A free air, or 250A bundled.
A 185 mm2 Cu cable is rated just over 400A
Agree with GordMay as to favoring towards utilization of conservative ratings.
Same holds true for selection of ground tackle. Big is good.

The single 95 mm2 cable does appear to be very inadequate for the apparent DC current draw of 400 amps. Not sure what the temperature rating of the insulation of the cable is on this vessel. Assuming 60 C rubber, then it's DC ampacity may be only 258. A higher temperature insulation would provide for higher ampacity but the conductor will nonetheless be hot, just the rubber will not be as inclined to melt.

I2R analysis:

258 Amps X 258 Amps = 66,564 versus 400 X 400 = 160,000

Reference http://www.aeicables.co.uk/literatur...entRatings.pdf

Snipet therefrom copied and attached below.

From looking at the picture of the fuse holder the washer does appear to be on the outside [nut side] of the ANL. Washers make for great resistors so don't place them between the fuse and the holder.

Can't be certain but there appears to be some heat stress to the block of the ANL holder, OP should examine to see if it has been cooked and in need replacement.

I hate dealing with low voltage high amperage power sourcing. 12V DC being such a poor legacy, but there you go.
Attached Thumbnails
Click image for larger version

Name:	ampacity.PNG
Views:	239
Size:	189.1 KB
ID:	183857  
Montanan is offline   Reply With Quote
Old 15-01-2019, 09:43   #13
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,496
Re: ANL Fuse/holder getting real hot

What in the world are you doing with a five kW load at 12 volts? Have you considered upgrading to 24 volts or running a generator to supply that load rather than an inverter? What is the capacity of your battery bank?
stormalong is offline   Reply With Quote
Old 15-01-2019, 09:53   #14
Registered User

Join Date: Oct 2014
Posts: 7,310
Re: ANL Fuse/holder getting real hot

Can't see the entire system layout, but there appears to be negative cables in contact by crossing positive cables. If such contacts [e.g, crossings] of opposite polarity are on non-fuse protected circuitry, i.e., towards the DC battery source and not down circuit of the DC fuse that would be inappropriate layout of cabling and not to standard.

Only a safety issue if and when the insulation breaksdown or wears due to rubbing. I see cable ties on some of the cables which forces the cables to touch.
Montanan is offline   Reply With Quote
Old 15-01-2019, 10:26   #15
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,662
Re: ANL Fuse/holder getting real hot

That is a lot of amperage.

If it were me, after re-evaluating the wiring rating, connectors, etc., I would consider replacing the ANL fuse block with a more robust Class T block and fuse.

Best wishes getting ahead of that potentially dangerous sutuation.

Cheers! Bill
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
DIY ANL Fuse Block? Delancey Electrical: Batteries, Generators & Solar 39 29-11-2016 16:03
ANL Fuse holders Kakalina Electrical: Batteries, Generators & Solar 8 25-10-2016 08:07
For Sale: Blue Sea Systems ANL fuse block, Buss 100 amp circuit breaker Pauliboi Classifieds Archive 0 06-11-2015 13:07
500 amp ANL fuse stud size? sdowney717 Electrical: Batteries, Generators & Solar 6 24-02-2013 14:04
ANL Fuse to Starter Down2TheC Electrical: Batteries, Generators & Solar 3 22-08-2009 21:18

Advertise Here


All times are GMT -7. The time now is 01:36.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.