Re: Advice Needed: Step UP transformer for Land Power

Quote:
Originally Posted by skipmac View Post
So the fact that the voltage on US 240 v 3 wire system is 180 out of phase on the two hot wires doesn't cause any problem on 220/230 V EU 50 Hz equipment?

What about the opposite. If the equipment would tolerate the 50 Hz frequency would US 240 V equipment run on EU 230 V supply?

split phase systems are not "out of phase", if one takes the waveform from the perspective of the two hot wires, then all you have is 240VAC single phase.

If one takes it from ground or neutral, one sees a "out of phase " system, its however a measurement delusion.

A EU cooker ( range) on US splitphase, will see exactly the same potential waveform as that cooker on a floating neutral EU supply.

Yes there are specific safety issues, for example the assumption on an EU boat that "neutral" is at ground or near ground can cause issues.

Frequency and certain safety installation issues aside, there is no issue.


Again the reverse is true, leaving aside some safety issues with very old US 240 equipment


so as long as the frequency is an issue ( generally with some motors) its all the same type of electrons !!!



dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 22-09-2014, 06:23   #17
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Advice Needed: Step UP transformer for Land Power

Wow....

The incredibly rare triple post....

New mod Weevis must be on watch duty...
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 22-09-2014, 08:03   #18
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Advice Needed: Step UP transformer for Land Power

Quote:
Originally Posted by clifflyon View Post
Hi All

I just bought a Benetoooo' 50 (New Life) with a 220V 30 amp 50Hz system.

Im told I should aquire a step-up transformer to 240v 60 Hz just to be safe on U.S./Caribbean land power ( I plan to cruise the Carib for year-plus).

I'm hanging in a marina in Key Biscayne till Nov 1, plugged into 240 60 hrz. Everything seems to run fine at the moment. The surveyor urged me to deal with this issue.

Do I really need such a thing and if so what do you recommend? My most excellent electrical guru says I need something to handle at least 6000 watts.

You can probably get a buck boost transformer at a local electrical supplier.

Changing from 50 to 60 Hz is going to be close to impossible without very deep pockets. I don't believe it will effect much other than the speed of any synchronous motors on board.

For what it may or may not be worth.

Cliff
Cadence is offline   Reply With Quote
Old 22-09-2014, 08:57   #19
Registered User

Join Date: Mar 2013
Location: west coast of Thailand
Boat: Mason 44
Posts: 226
Re: Advice Needed: Step UP transformer for Land Power

Hi Cliff

I bought a boat with a 110v 60 hz genset in SEA EU240v 50hz. .

On shore power 240v 50hz, the step down transformer to 120v 50hz can run

- 120v microwave
- 120v water heater
- 120v Marine Air ac 16,000 btu
- 120v water maker, booster pump and 120v
- 120v coffee grinder

On the hook when everything runs off the inverter or genset for 120v 60Hz with a step up transformer 240v 60hz can run

- 240v rice cooker
- 240v juicer/food processor
- 240v kettle
- 240v power drill

All the computer power supply and hand phone chargers handle both 120v and 240v.

I am sure there will be something that won't work on 240v 60hz. so far most items I use, works.
ericoh88 is offline   Reply With Quote
Old 22-09-2014, 10:12   #20
Registered User
 
clifflyon's Avatar

Join Date: Jun 2014
Location: Luperon, DR
Boat: Beneteau 440 sv Yenrah II
Posts: 55
Send a message via Skype™ to clifflyon
Re: Advice Needed: Step UP transformer for Land Power

Thanks all !!!! What an excellent resource this forum. Centuries of combined experience and wisdom. Invaluable!

SO, does anyone know where I can have a 1999 Simpson Lawrence electric Capstan/windlass rebuilt in the Miami areas?

Thanks AGAIN!

Cliff
clifflyon is offline   Reply With Quote
Old 22-09-2014, 11:45   #21
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Advice Needed: Step UP transformer for Land Power

Quote:
Originally Posted by clifflyon View Post
Thanks all !!!! What an excellent resource this forum. Centuries of combined experience and wisdom. Invaluable!

SO, does anyone know where I can have a 1999 Simpson Lawrence electric Capstan/windlass rebuilt in the Miami areas?

Thanks AGAIN!

Cliff
What needs rebuilding on the windlass? Job isn't that complicated unless the new ones are a lot trickier than the old ones. I totally stripped down my 1994 SL, repainted, new bearings, lubed up, rewired and installed a new switch. Wasn't much more complicated that a small jigsaw puzzle.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 22-09-2014, 14:15   #22
Registered User
 
clifflyon's Avatar

Join Date: Jun 2014
Location: Luperon, DR
Boat: Beneteau 440 sv Yenrah II
Posts: 55
Send a message via Skype™ to clifflyon
Re: Advice Needed: Step UP transformer for Land Power

Quote:
Originally Posted by skipmac View Post
What needs rebuilding on the windlass? Job isn't that complicated unless the new ones are a lot trickier than the old ones. I totally stripped down my 1994 SL, repainted, new bearings, lubed up, rewired and installed a new switch. Wasn't much more complicated that a small jigsaw puzzle.
Motor works but the gear doesn't engage up or down. I'm guessing a pin is sheered. I need to find a puller.

Tomorrow...
clifflyon is offline   Reply With Quote
Old 22-09-2014, 19:49   #23
Registered User

Join Date: Sep 2013
Location: Alert Bay, Vancouver Island
Boat: 35ft classic ketch/yawl.
Posts: 1,984
Images: 4
Send a message via Skype™ to roland stockham
Re: Advice Needed: Step UP transformer for Land Power

My solution to converting from 230v electrics (European) to other systems was simple. I have an inverter so use that as the ONLY mains voltage supply on board. Then fitted a 40amp universal voltage charger to keep the battery topped up. Result; any frequency and voltage in, totally stable output with full isolation even with reverse phase and other dock side horrors. Charger needs to give 10% more power per day than your expected total A/C and D/C power needs. Its better than an isolation transformer because you always get the right Hz on board and much cheaper. Only limit is the size of your inverter (get a low power kettle!)
roland stockham is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Step down transformer for sale hooligan6a Classifieds Archive 5 26-12-2011 15:45
For Sale: Brushing Awlgrip — A Step by Step Video Guide dennisjay Classifieds Archive 2 17-05-2011 11:54
Step-by-Step - for Dummies . . . Jimbo2010 OpenCPN 7 30-09-2010 18:43

Advertise Here


All times are GMT -7. The time now is 16:18.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.