Ac voltage drop?

On our newnto us leopard 38, I have noticed the ac line in volt meters drop from about 110ish to 100-105. When the ac unit kicks on. We have fairly long (50ft) shore power cords. Both lines in seem to do it. Is this normal?
__________________

__________________
Dulcesuenos is offline   Reply With Quote
Old 04-02-2014, 19:21   #2
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,429
Re: Ac voltage drop?

Look at the ends of your shore power cords and feel them when the AC is running. You might have a bad connection that is burning the end or heating it and it soon will be burnt.

The problem can be just as much in the socket end as the cord end. If that is your problem, replace it all.

David
__________________

__________________
djmarchand is offline   Reply With Quote
Old 04-02-2014, 19:23   #3
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,432
Re: Ac voltage drop?

http://www.bestboatwire.com/voltage-drop-calculator

A guess would be the dock wiring is undersized for it's length. At 20a your cables will lose ~2v.
__________________
DotDun is offline   Reply With Quote
Old 04-02-2014, 19:23   #4
Nearly an old salt
 
goboatingnow's Avatar

Cruisers Forum Supporter

Join Date: Jun 2009
Posts: 13,649
Images: 3
Re: Ac voltage drop?

Quote:
Originally Posted by djmarchand View Post
Look at the ends of your shore power cords and feel them when the AC is running. You might have a bad connection that is burning the end or heating it and it soon will be burnt.

The problem can be just as much in the socket end as the cord end. If that is your problem, replace it all.

David
Of course the problem might be from the shore power pillar back , back a long way !!!

Dave
__________________
Check out my new blog on smart boat technology, networking and gadgets for the connected sailor! - http://smartboats.tumblr.com
goboatingnow is offline   Reply With Quote
Old 04-02-2014, 20:07   #5
Registered User
 
Dulcesuenos's Avatar

Join Date: Dec 2010
Location: Florida Keys, Bahamas Bound
Boat: 38' French Cat
Posts: 2,828
Images: 4
Quote:
Originally Posted by DotDun View Post
http://www.bestboatwire.com/voltage-drop-calculator

A guess would be the dock wiring is undersized for it's length. At 20a your cables will lose ~2v.
Can this cause any damage or issues with our equipmemt?
__________________
Dulcesuenos is offline   Reply With Quote
Old 04-02-2014, 20:09   #6
Nearly an old salt
 
goboatingnow's Avatar

Cruisers Forum Supporter

Join Date: Jun 2009
Posts: 13,649
Images: 3
Re: Ac voltage drop?

Quote:
Originally Posted by Dulcesuenos View Post
Can this cause any damage or issues with our equipmemt?
Your daughters will spend slightly longer drying their hair !

Dave
__________________
Check out my new blog on smart boat technology, networking and gadgets for the connected sailor! - http://smartboats.tumblr.com
goboatingnow is offline   Reply With Quote
Old 04-02-2014, 20:13   #7
Marine Service Provider

Join Date: Oct 2011
Posts: 1,205
Re: Ac voltage drop?

The V-drop may be caused by poor PowerFactor aka PF. Do you have the specs on the AirCon? Many older units, ie more then 4 years old PF near unity wasn't mandated. It is now mandated on new units.

Use a good quality True RMS meter with Htz setting. put the prongs in an ac outlet onboard. It should read 60-61 cycles. Now turn on the AC, and if the cycles drop it's a power factor issue.

Lloyd

Quote:
Originally Posted by Dulcesuenos View Post
On our newnto us leopard 38, I have noticed the ac line in volt meters drop from about 110ish to 100-105. When the ac unit kicks on. We have fairly long (50ft) shore power cords. Both lines in seem to do it. Is this normal?
__________________
FlyingCloud1937 is offline   Reply With Quote
Old 04-02-2014, 22:43   #8
Registered User
 
irwin37's Avatar

Join Date: Oct 2009
Location: Gettysburg Pa
Boat: 1981 Irwin 37
Posts: 193
Re: Ac voltage drop?

I don't mean to knock anyone but PF or power factor has nothing to do with the frequency (60 HTZ). Power factor is the difference between true and apparent power used. A device with low power factor (< 1.0) will draw more current and cost more to run. You are most likely seeing a voltage drop caused by bad connections or dock wiring as pointed out before. Running equipment on a voltage lower than specified can caused early motor or compressor failure as they will tend to draw more current at lower voltages and run hotter.

John
__________________
irwin37 is offline   Reply With Quote
Old 04-02-2014, 23:18   #9
Marine Service Provider

Join Date: Oct 2011
Posts: 1,205
Re: Ac voltage drop?

Bad PF will magnify the V-drop, and connection issues.

From the grid it will be overcome, but from a generator, the cycle drop will not be able rebound.

So one step at a time.

I'm just trouble shooting... one by one. If I try to lay it out all at once it would be over-whelming.

Lloyd

Quote:
Originally Posted by irwin37 View Post
I don't mean to knock anyone but PF or power factor has nothing to do with the frequency (60 HTZ). Power factor is the difference between true and apparent power used. A device with low power factor (< 1.0) will draw more current and cost more to run. You are most likely seeing a voltage drop caused by bad connections or dock wiring as pointed out before. Running equipment on a voltage lower than specified can caused early motor or compressor failure as they will tend to draw more current at lower voltages and run hotter.

John
__________________
FlyingCloud1937 is offline   Reply With Quote
Old 04-02-2014, 23:21   #10
Marine Service Provider

Join Date: Oct 2011
Posts: 1,205
Re: Ac voltage drop?

So yes, V-drop is current related. and PF is an issue.

Lloyd

Quote:
Originally Posted by irwin37 View Post
I don't mean to knock anyone but PF or power factor has nothing to do with the frequency (60 HTZ). Power factor is the difference between true and apparent power used. A device with low power factor (< 1.0) will draw more current and cost more to run. You are most likely seeing a voltage drop caused by bad connections or dock wiring as pointed out before. Running equipment on a voltage lower than specified can caused early motor or compressor failure as they will tend to draw more current at lower voltages and run hotter.

John
__________________
FlyingCloud1937 is offline   Reply With Quote
Old 05-02-2014, 06:36   #11
Senior Cruiser
 
colemj's Avatar

Cruisers Forum Supporter

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,049
Images: 12
Re: Ac voltage drop?

Power factor on a single boat means absolutely nothing to a commercial power grid. Unless the OP was talking about running off his generator, the PF is meaningless to his issue.

We experience this often in many marinas and it is related to the quality and condition of their wiring/power. However, the marinas we are in are often wired with whatever wire is available and strung through the water with multiple connections, etc - so these power drops are understandable.

I would expect US marinas wired to code to be better.

Mark
__________________

__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 14:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.