AC Grounding, w outboard ??

Well here I go, throw my self into the wolves. I understand how AC works but here is the dilema. I want 2 AC outlets for when I am at the dock only. DC only for the weekend cruises. Is it safe to be connected to the GRD on the dock only or where else would I GRD to? Boat has an outboard only which is not in the water all the time, it is stowed and pull start. So feel free to give me your two. Thanks

Adam
awr401 is offline   Reply With Quote
Old 05-03-2009, 00:00   #2
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,961
assuming no inverter in the boat, in your situation, you can install that completely insulated from everything. Install a shore-power inlet. Install a ground-fault protection device and wire it to the power inlet on it's input and the two outlets on it's output. Use 3 wires everywhere.

Think about battery charger. Use a portable charger with cord into outlet if your battery bank is small enough for the charger to handle.

cheers,
Nick.
s/v Jedi is offline   Reply With Quote
Old 05-03-2009, 04:03   #3
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,384
Images: 241
Assuming your dock has a proper 30A 120V Twist-Lok Shore Power Outlet (receptacle), one simple solution would be to:
Your 30A (3 - #10)cord will plug into your 30A twist-lok Inlet (on boat)
Wired (3 - #10AWG) to a 2Pole 15A Breaker, wired (3 - #12 or #14) to a 15A GFCI Recptacle, then to the second standard receptacle.
The Black Hot wires are connected to the breaker and brass terminals.
The White Neutrals are connected to the breaker and silver terminals.
The Green Ground wires are connected to the green grond terminals, which are isolayted (not connected to anything else).

Excerpted from ABYC E-11

11.7.2.2.1.1. The shore grounded (white) and
ungrounded shore current carrying conductors are
connected from the shore power inlet to the boat's AC
electrical system through an overcurrent protection
device that simultaneously opens both currentcarrying
conductors. Fuses shall not be used instead of
simultaneous trip devices. (See E-11.12.2.9.2.)

11.7.2.2.1.2. Neither the shore grounded
(white) neutral conductor nor the ungrounded current
carrying conductors shall be grounded on the boat.
(See E-11.5.3.2.1.)

11.7.2.2.1.4. The shore-grounding (green)
conductor is connected, without interposing switches
or overcurrent protection devices (See E-11.5.3.5.),

11.7.2.2.1.4.1. an optional galvanic isolator, and
then to

11.7.2.2.1.4.2. all non-current carrying parts of
the boat’s AC electrical system, including

11.7.2.2.1.4.3. the engine negative terminal or its
bus.

11.7.2.2.1.5. If an optional galvanic isolator is
used, the shell of a metallic shore power inlet shall be
electrically insulated from the boat.

11.7.2.2.1.6. If the boat's AC electrical system
includes branch circuit breakers, the branch circuit
breakers shall simultaneously open both current
carrying conductors unless a polarity indicating device
is provided. (See E-11.12.2.6.1 Exception.)

See Diagram 1 on page 11 at:
http://www.abycinc.org/committees/.%5CE-11.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 05-03-2009, 05:56   #4
Registered User

Join Date: Feb 2009
Boat: 1968 Columbia 28 "KEOLA O KE KAI"
Posts: 12
I thought I was overthinking it, but thanks for the guidance. I was thinking of having an inverter but have no need for it away from dock. I wasn't sure if I need a grounding plate or what? Just confused by myself more than anything,

Mahalo
awr401 is offline   Reply With Quote
Reply

Tags
outboard

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mercury outboard book? Or just outboard? Jack Long The Library 2 17-09-2008 08:33
Grounding question prout35 Electrical: Batteries, Generators & Solar 3 09-07-2008 10:50
Grounding without an Engine Aqua Vitae Electrical: Batteries, Generators & Solar 13 06-07-2008 19:05
Grounding all throughulls? Zach Construction, Maintenance & Refit 23 07-12-2007 15:12
The Robertson II grounding knottybuoyz Health, Safety & Related Gear 4 13-07-2007 12:29

Advertise Here


All times are GMT -7. The time now is 16:40.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.