A/C Start Up on Generator

I have a problem: the A/C would not start on the generator
A/C is old Cruis'air (probably 15k BTU, I'm not sure) the generator is 3300 nominal and 3600 peak, 120v 30A.

I was told that I need to put a relay and capacitor for the surge at start up and that will solve the problem
Also that a delay in the water pump start will help.

Can anybody help me with more details and explain a little more what I have to do in order to have the A/C starting correctly under generator?

Thank you
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 06-06-2011, 08:58   #2
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,060
Re: A/C Start Up on Generator

I had the same problem. What you need is called a "Hard Start Capacitor". They are made by Supco. Here is a link: http://www.supco.com/images/pdfs/200...ion%202-51.pdf
They are very easy to install. If you look at the label on your AC compressor you will see a number called Locked Rotor Amps or LRA. This is very close to the number of amps you will need to start the compressor. It can be eight or ten times the amps required to run it. The hard start capacitor stores up energy and then gives out a burst to kick the compressor into motion. I think newer ACs are coming with these already installed. My little 5000 BTU AC needs over 3000 watts to start. With the hard start capacitor installed I can start and run it on a little 1000 watt Honda.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 06-06-2011, 09:00   #3
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by HopCar View Post
I had the same problem. What you need is called a "Hard Start Capacitor". They are made by Supco. Here is a link: http://www.supco.com/images/pdfs/200...ion%202-51.pdf
They are very easy to install. If you look at the label on your AC compressor you will see a number called Locked Rotor Amps or LRA. This is very close to the number of amps you will need to start the compressor. It can be eight or ten times the amps required to run it. The hard start capacitor stores up energy and then gives out a burst to kick the compressor into motion. I think newer ACs are coming with these already installed. My little 5000 BTU AC needs over 3000 watts to start. With the hard start capacitor installed I can start and run it on a little 1000 watt Honda.
THANKS A LOT!!
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 06-06-2011, 09:03   #4
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,060
Re: A/C Start Up on Generator

You're very welcome. Let me know how it works out. You can probably buy the hard start kit locally from a refridgeration supply house. They aren't expensive.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 06-06-2011, 15:25   #5
Registered User
 
Vyndance's Avatar

Join Date: Mar 2010
Location: Ventura, CA
Boat: 48 Californian
Posts: 195
Images: 12
Re: A/C Start Up on Generator

Is this a new install or has it worked in the past?
Vyndance is offline   Reply With Quote
Old 06-06-2011, 20:38   #6
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Gen is new. A/C was there already.
Will install a Supca Hard start SSP 6 as soon as possible
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 06-06-2011, 21:22   #7
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: A/C Start Up on Generator

There are also capacitor start motors in case the first solution does not work.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 13-06-2011, 12:06   #8
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

We tried SSP6 doesn't work...
A/C specialist recommend installing the Crusair "soft start" kit. Not cheap.. but the Admiral will be happy if we managed to have the A/C working.
Somebody suggested that the gen being new, the engine has to be broken down a few 10 hrs before having really an opinion... ??? I'm puzzled by the comment
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 14-06-2011, 05:27   #9
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

The soft start kit will be installed next Friday.. let's hope the problem will be solved.
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 14-06-2011, 05:38   #10
Registered User

Join Date: May 2008
Posts: 3,536
Re: A/C Start Up on Generator

If the soft start doesn't work, another solution is something like a Victron Inverter/Charger. These can use the inverter to provide extra power from the batteries while passing through the the power from the genset. Since it's only for a second, the batteries have more than enough capacity.

This only makes sense if you need a new inverter/charger. Of course, this is even more money to solve a problem that doesn't seem like it should have been a problem in the first place. But this is a boat......

Carl
CarlF is offline   Reply With Quote
Old 14-06-2011, 05:46   #11
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by CarlF View Post
If the soft start doesn't work, another solution is something like a Victron Inverter/Charger. These can use the inverter to provide extra power from the batteries while passing through the the power from the genset. Since it's only for a second, the batteries have more than enough capacity.

This only makes sense if you need a new inverter/charger. Of course, this is even more money to solve a problem that doesn't seem like it should have been a problem in the first place. But this is a boat......

Carl
Thanks
Where can I get more details on this?
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 14-06-2011, 08:27   #12
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: A/C Start Up on Generator

Quote:
Originally Posted by Alecadi View Post
Thanks
Where can I get more details on this?
It's called "Power Assist":

Quote:
Power connections to provide all the power you need are not always available. That’s why Victron Energy developed Power Assist. This feature monitors power consumption and supplies additional power to prevent overloading. The Quattro can temporarily turn a 16A connection into 38A and a 5kVA generator into 10kVA. No other brand offers better functionality in this arena than the inventor: Victron Energy.
ciao!
Nick.
s/v Jedi is offline   Reply With Quote
Old 14-06-2011, 08:54   #13
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by s/v Jedi View Post
It's called "Power Assist":



ciao!
Nick.
Thanks Nick
Alec
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 14-06-2011, 09:08   #14
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,572
Re: A/C Start Up on Generator

If this is a new installation, follow the above. If this is an old, clean and reconnect ALL wires from the generator to the Ac unit. Mine was having trouble starting, and I found a 40volt drop from generator to AC during startup. New connectors fixed this.
capn_billl is offline   Reply With Quote
Old 16-06-2011, 09:32   #15
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

We isntalled the soft start but doesn't work either
and yes we have a voltage drop of more than 30v...
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator vs Inverter Generator (Genset) Jon4399 Electrical: Batteries, Generators & Solar 30 11-01-2011 09:13
Fault with First Start of Generator ? kerry231168 Electrical: Batteries, Generators & Solar 5 04-12-2010 08:38
Portable Generator vs Solar Panels or Wind Generator Sweet As Electrical: Batteries, Generators & Solar 120 16-09-2010 18:27
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06

Advertise Here


All times are GMT -7. The time now is 07:52.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.