Re: A/C Start Up on Generator

I agree with installing a hard start capacitor. I like the solid state ones, but you'll need the right one for your specific compressor motor. Make sure you test the voltage - amperage at the compressor terminals with the genset running and shore power off to see if it's an electrical problem first; IE wrong wire size or connection corrosion.
__________________

Seahunter is offline   Reply With Quote
Old 17-06-2011, 06:00   #17
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by Seahunter View Post
I agree with installing a hard start capacitor. I like the solid state ones, but you'll need the right one for your specific compressor motor. Make sure you test the voltage - amperage at the compressor terminals with the genset running and shore power off to see if it's an electrical problem first; IE wrong wire size or connection corrosion.
I don't know if I understand you well
But we tested also with the shore power and there is almost no drop in voltage and the compressor start without problem
The unit is old (was an option originally in the boat- 1984) but is working perfectly and I don't want to change it for something newer.
But the start up with the gen is the problem
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 06:20   #18
Registered User
 
DeepFrz's Avatar

Cruisers Forum Supporter

Join Date: Mar 2006
Location: Winnipeg
Boat: None at this time
Posts: 8,462
Re: A/C Start Up on Generator

So, if there is no drop in voltage when starting the A/C from shore power, and a 30 volt drop when starting from the generator, where is that voltage being dropped? Perhaps the generator wiring, perhaps a connection.
DeepFrz is offline   Reply With Quote
Old 17-06-2011, 06:34   #19
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,461
Re: A/C Start Up on Generator

You can't compare AC voltage drop from shorepower and voltage drop from a genset.

Shorepower voltage drop is mostly dependent on the size of the wire going back to the shorepower outlet and the wiring size upstream from there. The grid has effectively unlimited current supply capability.

But a genset in addition to the wire voltage drop has additional voltage drop in its windings and as the genset speed drops due to the engine not having enough torque.

But having said all of the above, if you have installed Dometic's Smart Start system which significantly reduces inrush current and your A/C still won't start, then you most likely have a problem with the wiring to your genset or the genset itself.

One test that you can do that isn't very expensive: Disconnect the A/C supply from the genset downstream from the breaker protecting the genset. You should have a breaker within sight distance of the genset to meet NEC. Go to Home Depot or Lowes and buy enough #10 2 conductor plus ground Romex cable to go from that breaker to the A/C. Wire it to your A/C and try starting it. #10 is bigger than it needs to be but will completely eliminate wiring, connections and other breakers as a cause.

If it still won't start then the problem lies in your genset.

David
djmarchand is offline   Reply With Quote
Old 17-06-2011, 06:56   #20
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by djmarchand View Post
One test that you can do that isn't very expensive: Disconnect the A/C supply from the genset downstream from the breaker protecting the genset. You should have a breaker within sight distance of the genset to meet NEC. Go to Home Depot or Lowes and buy enough #10 2 conductor plus ground Romex cable to go from that breaker to the A/C. Wire it to your A/C and try starting it. #10 is bigger than it needs to be but will completely eliminate wiring, connections and other breakers as a cause.

If it still won't start then the problem lies in your genset.

David
WOUAW
you've lost me there
can you explain in lay terms please so that I can understand it
Thank you
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 06:59   #21
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by djmarchand View Post
You can't compare AC voltage drop from shorepower and voltage drop from a genset.

Shorepower voltage drop is mostly dependent on the size of the wire going back to the shorepower outlet and the wiring size upstream from there. The grid has effectively unlimited current supply capability.

But a genset in addition to the wire voltage drop has additional voltage drop in its windings and as the genset speed drops due to the engine not having enough torque.

But having said all of the above, if you have installed Dometic's Smart Start system which significantly reduces inrush current and your A/C still won't start, then you most likely have a problem with the wiring to your genset or the genset itself.

One test that you can do that isn't very expensive: Disconnect the A/C supply from the genset downstream from the breaker protecting the genset. You should have a breaker within sight distance of the genset to meet NEC. Go to Home Depot or Lowes and buy enough #10 2 conductor plus ground Romex cable to go from that breaker to the A/C. Wire it to your A/C and try starting it. #10 is bigger than it needs to be but will completely eliminate wiring, connections and other breakers as a cause.

If it still won't start then the problem lies in your genset.

David
The genset is a external portable set
It is connected to the same marine plug as the shore power would.
So from there the wiring is exactly the same. Going to the AC power panel etc...
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 08:02   #22
Registered User

Join Date: Jul 2009
Posts: 774
Re: A/C Start Up on Generator

Quote:
Originally Posted by Alecadi View Post
I don't know if I understand you well
But we tested also with the shore power and there is almost no drop in voltage and the compressor start without problem
The unit is old (was an option originally in the boat- 1984) but is working perfectly and I don't want to change it for something newer.
But the start up with the gen is the problem
I guess this was a test. I assumed, probably wrongly that someone has tested the amperage rating of the genset. If the AC works with shorepower, but not with the genset, the genset is probably too small. If the genset is dropping voltage at startup, it's because it's trading votlage for amperage it doesn't have. What is the brand, make and model of the genset?
__________________

Seahunter is offline   Reply With Quote
Old 17-06-2011, 08:11   #23
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

Quote:
Originally Posted by Seahunter View Post
I guess this was a test. I assumed, probably wrongly that someone has tested the amperage rating of the genset. If the AC works with shorepower, but not with the genset, the genset is probably too small. If the genset is dropping voltage at startup, it's because it's trading votlage for amperage it doesn't have. What is the brand, make and model of the genset?
As stated in this thread in anterior posting the gen is a 3600 w
should be enough
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 08:21   #24
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,059
Re: A/C Start Up on Generator

It's really starting to sound like the generator isn't putting out what it is rated for.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 17-06-2011, 08:36   #25
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

The generator people are very helpful: they just send me the way to solve the problem.
There is a tuning to do on the generator to solve this drop in voltage.
I put in attachement what they send me right now.
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 08:37   #26
Registered User

Join Date: May 2008
Posts: 3,536
Re: A/C Start Up on Generator

You've got a big air conditioner (15K BTU) on a small genset (3.6KW). And they're old. New technology compressors are easier starting than old but a current Cruiseair 16kBTU unit draws 10.4 amps running and has a "locked rotor" draw of 62 amps.

It wouldn't surprise me if your air conditioner briefly draws over 40 amps when starting. Even today, gensets have "optimistic" capacities. Once you're over 80% load, voltage and even frequency can start to vary.

The Victron inverter/charger (Mastervold makes a similar unit I believe) isn't cheap - about $2300 - but it will solve this problem, as well as take great care of your batteries, and give you high quality sine wave 110v power.

Another advantage is that they can be set to not overload your genset which can really shorten its life. I have mine set to never draw more than 80% of the max capacity. The Victron uses the batteries to make up any short term shortage. Same with shore power. I never pop a shore power breaker because I set the Victron to limit the draw on a 30amp service to 27 amps.

MultiPlus 800VA - 5kVA - Victron Energy

Carl
CarlF is offline   Reply With Quote
Old 17-06-2011, 08:38   #27
Registered User

Join Date: Jul 2009
Posts: 774
Re: A/C Start Up on Generator

Quote:
Originally Posted by Alecadi View Post
As stated in this thread in anterior posting the gen is a 3600 w
should be enough
Yes I read that. I asked what make, model it was. But as you previously stated it is 3600 peak. The genset's probably too small to get through all the wiring you have and even if you wired it directly to the AC unit it might start as unlike fridges, AC units start under load. Adjusting the voltage peak on idle won't fix the problem; only a bigger genset. A genset's amperage is like a bottle of water, it can hold only so much and this adjustment isn't going to allow you to add more water.
__________________

Seahunter is offline   Reply With Quote
Old 17-06-2011, 09:37   #28
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,461
Re: A/C Start Up on Generator

Sorry, didn't realize that it wasn't a permanently installed genset.

Reading between the lines of the attachment you posted, I think you have a Chinese made generator/inverter, like the Honda EU series. For maximum power and voltage output, set the econo switch to off. This lets the engine run at maximum rpm and power.

David
djmarchand is offline   Reply With Quote
Old 17-06-2011, 10:33   #29
Registered User
 
Alecadi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: Marathon FL
Boat: Endeavour 35, 1984,
Posts: 937
Re: A/C Start Up on Generator

To David: YES the econo was off all the time.. :-)
To CarlF: a bigger genset would be too much, I would not even be able to put it on desk!!
To all: have you seen what the gen people send me to solve the problem (see post#25) ? Any comments or recommendation?
__________________
People spend time putting little boats in bottles, me I put bottles in my little boat...
Alecadi is offline   Reply With Quote
Old 17-06-2011, 10:52   #30
Registered User

Join Date: Sep 2007
Location: FL
Boat: Pacific Seacraft 31 - Cielo Azul
Posts: 360
Images: 3
Re: A/C Start Up on Generator

My experience is with a Frigidare 5000 BTU AC and Honda 1000 is:
normal amp draw when running is ~5amps (it starts around 4.8 and slowly climbs to 5.2 for some reason).
When set on low, Fan draws about .5 amps, but when compressor kicks in it goes up to 14 amps, the gen has a 4 second delay before disconnecting, with eco-throttle on, sometimes it recovers in 4 seconds and sometimes it doesn't.
One thing I can't explain, when set to high, the draw is the same, I'm using kill-a-watt to measure the amps.
Tom
teejayevans is offline   Reply With Quote
Reply

Tags
generator

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator vs Inverter Generator (Genset) Jon4399 Electrical: Batteries, Generators & Solar 30 11-01-2011 09:13
Fault with First Start of Generator ? kerry231168 Electrical: Batteries, Generators & Solar 5 04-12-2010 08:38
Portable Generator vs Solar Panels or Wind Generator Sweet As Electrical: Batteries, Generators & Solar 120 16-09-2010 18:27
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06

Advertise Here


All times are GMT -7. The time now is 16:19.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.