6 T-105 OR 4 TROJAN J305E-AC?

I am trying to decide how much battery to add. Based on 530 watts of solar, can can easily fit 4 of the J305E-AC ( 305 AHr) or with difficulty, 6 of the T-105. Previously, we had 270 watts and 359 AHr of gel cells so even 2 of the T-105s are a 25% improvement. We expect to use about 20% more electricity on the new boat. Is 530 watts too much for 450 AHr? The J305 are a 20% premium per annualized AHr/life cycle.

Also looked at the Duracell EGC2 (230 AHr) - they are 20% less than the T-105 and slight shorter ( = less space under the plates?) Gets confusing quickly.
Sailorman Ed is offline   Reply With Quote
Old 07-12-2015, 19:05   #2
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by Sailorman Ed View Post
I am trying to decide how much battery to add. Based on 530 watts of solar, can can easily fit 4 of the J305E-AC ( 305 AHr) or with difficulty, 6 of the T-105. Previously, we had 270 watts and 359 AHr of gel cells so even 2 of the T-105s are a 25% improvement. We expect to use about 20% more electricity on the new boat. Is 530 watts too much for 450 AHr? The J305 are a 20% premium per annualized AHr/life cycle.

Also looked at the Duracell EGC2 (230 AHr) - they are 20% less than the T-105 and slight shorter ( = less space under the plates?) Gets confusing quickly.
Six T-105s will give you 675AH capacity. I'd go with that.

Bill
btrayfors is offline   Reply With Quote
Old 07-12-2015, 19:27   #3
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by Sailorman Ed View Post
I am trying to decide how much battery to add. Based on 530 watts of solar, can can easily fit 4 of the J305E-AC ( 305 AHr) or with difficulty, 6 of the T-105. Previously, we had 270 watts and 359 AHr of gel cells so even 2 of the T-105s are a 25% improvement. We expect to use about 20% more electricity on the new boat. Is 530 watts too much for 450 AHr? The J305 are a 20% premium per annualized AHr/life cycle.

Also looked at the Duracell EGC2 (230 AHr) - they are 20% less than the T-105 and slight shorter ( = less space under the plates?) Gets confusing quickly.
You do know that batteries you mention are 6v?

(2) T-105's are only 225ah @ 12v.
DotDun is offline   Reply With Quote
Old 07-12-2015, 19:48   #4
Registered User

Join Date: May 2012
Location: Hailing Minny, MN
Boat: Vancouver 27
Posts: 1,090
Images: 1
Re: 6 T-105 OR 4 TROJAN J305E-AC?

I recently ditched 3 group31 AGMs (270AH) for 2 Trojan J185Ps at (410AH). The high profile 185s fit well in my space and actually take up a significantly smaller footprint than the 31s used to.

If you have the height, L16s are also worth a look.

If budget is not overriding priority, why not take some measurements and go with whatever will fit the best for you?
laika is offline   Reply With Quote
Old 08-12-2015, 05:37   #5
Registered User
 
Sailorman Ed's Avatar

Join Date: Jun 2010
Boat: Gemini 105Mc+
Posts: 920
Images: 15
Send a message via Skype™ to Sailorman Ed
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Six T-105s will give you 675AH capacity
Bill - well 4 of the J305E will give almost as much and fit better but I have not seen anyone using these for some reason

Quote:
You do know that batteries you mention are 6v?

(2) T-105's are only 225ah @ 12v.
Yes, quite aware of voltage and 4 of them will provide 450 AH I was wondering if 450 is enough and a good match for the solar panel wattage

Quote:
I recently ditched 3 group31 AGMs (270AH) for 2 Trojan J185Ps at (410AH).
I will take a look at the J185. The L16s look great but are a bit pricey
I can squeeze in 6 of the T105 but will be a hassle with the cabling, this is why I considered 4 of the large capacity. Cost (and freight) is higher on the larger, less available batteries.
Sailorman Ed is offline   Reply With Quote
Old 08-12-2015, 07:08   #6
Moderator Emeritus
 
nigel1's Avatar

Cruisers Forum Supporter

Join Date: Oct 2009
Location: Manchester, UK
Boat: Beneteau 473
Posts: 5,591
Re: 6 T-105 OR 4 TROJAN J305E-AC?

I have just fitted 6 x T-125, same physical size as the 105's, but a few more Ah.
6 at 12V will give a theoretical 720Ah.
__________________
Nigel
Beneteau 473
Manchester, UK
nigel1 is offline   Reply With Quote
Old 08-12-2015, 08:25   #7
Registered User
 
S/V Alchemy's Avatar

Join Date: May 2008
Location: Nova Scotia until Spring 2021
Boat: Custom 41' Steel Pilothouse Cutter
Posts: 4,976
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by laika View Post
I recently ditched 3 group31 AGMs (270AH) for 2 Trojan J185Ps at (410AH). The high profile 185s fit well in my space and actually take up a significantly smaller footprint than the 31s used to.

If you have the height, L16s are also worth a look.

If budget is not overriding priority, why not take some measurements and go with whatever will fit the best for you?
This. You need to add the thickness of the box and any internal or external framing (I would consider L-bar, otherwise known as angle iron, coated in two-part epoxy and welded together save for bolted top bars). The L-16s are generally cheaper per Ah and more robust than the Trojans, which, while a very good battery, are not so much better as to justify their price premium in my opinion. The L-16s have thicker plates and are made for forklift and floor sweeper industrial use. Expect each pair to give you around 400 Ah @ 12 VDC, so four gives you 800 Ah at a weight of about 460 pounds.

If you have that much solar, and say a 100 amp alternator, you won't regret the extra capacity. Recall that the more time spent above the 50% SOC level, the better for the lifetime of the battery. But much depends on how you are able to store them.

Here's an example of a "basic brand" L-16 used in the solar home off-grid world: http://pdf.wholesalesolar.com/batter...ery/RE-L16.pdf
__________________
Can't sail? Read about our travels at https://alchemyonpassage.blogspot.com/. Can't sleep? Read www.alchemy2009.blogspot.com for fast relief. Can't read? Avoid www.volumesofsalt.blogspot.com, because it's just personal reviews of sea books.
S/V Alchemy is offline   Reply With Quote
Old 08-12-2015, 10:48   #8
Registered User

Join Date: Jan 2008
Location: Melbourne, Fl
Boat: Sail Craft, Apache 41
Posts: 40
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Industry says your output current of solar panels should be 5% - 13% of total amphr capacity of battery bank. Most use 10% as a rule of thumb.
Debgen is offline   Reply With Quote
Old 08-12-2015, 12:35   #9
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,678
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by Sailorman Ed View Post
I am trying to decide how much battery to add. Based on 530 watts of solar, can can easily fit 4 of the J305E-AC ( 305 AHr) or with difficulty, 6 of the T-105. Previously, we had 270 watts and 359 AHr of gel cells so even 2 of the T-105s are a 25% improvement. We expect to use about 20% more electricity on the new boat. Is 530 watts too much for 450 AHr? The J305 are a 20% premium per annualized AHr/life cycle.

Also looked at the Duracell EGC2 (230 AHr) - they are 20% less than the T-105 and slight shorter ( = less space under the plates?) Gets confusing quickly.
Ed, I've learned [after doing this several time on different boats over the decades...] to go for the maximum amp-hour capacity [and value in both $ and labor...] that fits in the space and budget at hand.

It sounds like your solar charging is suitable [6-7% of bank capacity; 10% the usual thumbnail target...] for either configuration you mention. [43A (I'm assuming regulated solar...) into a 610AH (J305E-AC) or 675AH (T105s) bank.]

As a comparative example, I was able to fit 8- T105s for a total of 900AH 12VDC @ the 20 hour rate. That size house banks suits us well, but I would welcome the chance to increase it if that battery form factor provides such an increase next time around...

Just FYI in case you don't already know (and I didn't until I researched it the time I upgraded my house bank batteries...) Trojan makes a very robust centralized watering system. [Hydrolink]

Let us know how you end up and have fun getting there.

Cheers!

Bill
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is offline   Reply With Quote
Old 08-12-2015, 13:00   #10
Registered User
 
Sailorman Ed's Avatar

Join Date: Jun 2010
Boat: Gemini 105Mc+
Posts: 920
Images: 15
Send a message via Skype™ to Sailorman Ed
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Trojan makes a very robust centralized watering system. [Hydrolink]
- thank Bill, I had seen it and if I go with the T105, I will have to use it due to space. With fewer L16s, I will have full easy access to the tops of the batts

Based on SV Alchemy's suggestion, I am looking seriously at the L16 size, just a bit more $$ and I suspect a much better battery and I can use fewer of them = less cabling. I do have wind (not yet installed) and since I am a cat, I must motor all the time as per the other thread so will pick up some from the alternator. We lived completely on 270 watts of solar last time and a smaller 359 AH battery bank ( 6-7 year old gel cells)

Also per Alchemy's suggestion, will be fabricating a better battery box but the 120 # L16 will take more than me to lift into position.
Sailorman Ed is offline   Reply With Quote
Old 08-12-2015, 23:07   #11
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by Sailorman Ed View Post
I am trying to decide how much battery to add. Based on 530 watts of solar, can can easily fit 4 of the J305E-AC ( 305 AHr) or with difficulty, 6 of the T-105. Previously, we had 270 watts and 359 AHr of gel cells so even 2 of the T-105s are a 25% improvement. We expect to use about 20% more electricity on the new boat. Is 530 watts too much for 450 AHr? The J305 are a 20% premium per annualized AHr/life cycle.

Also looked at the Duracell EGC2 (230 AHr) - they are 20% less than the T-105 and slight shorter ( = less space under the plates?) Gets confusing quickly.
Sounds like you are kinda going about managing your energy needs backwards.

1. Determine how many A-hrs per day you will consume.
2. Determine how many days you wish to go without recharging.
3. Determine how much battery capacity that requires (restricted by space and weight.)
4. Determine how quickly you wish to recharge (restricted by max acceptance rate of battery technology).
5. Select charging system(s) to add A-hrs at rate desired.

Max acceptance at percent of rated capacity:

Standard lead acid (25%)
Gel (40%)
AGM (60%)

Ramblin Rod
Yacht Service Provider
About Sheen Marine
ramblinrod is offline   Reply With Quote
Old 09-12-2015, 01:32   #12
Moderator Emeritus
 
nigel1's Avatar

Cruisers Forum Supporter

Join Date: Oct 2009
Location: Manchester, UK
Boat: Beneteau 473
Posts: 5,591
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Regarding the Hydrolink system, I have just fitted this to 6 Trojan batteries, and am impressed with the system, easy to fit and looks good quality.
Because two of my batteries are in a separate location I need to modify the system a bit and needed a second coupler. As Trojan only sell the whole kit, the coupler was purchased from
https://flow-rite.com/
at a reasonable price.
__________________
Nigel
Beneteau 473
Manchester, UK
nigel1 is offline   Reply With Quote
Old 09-12-2015, 12:26   #13
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,678
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by Sailorman Ed View Post
- thank Bill, I had seen it and if I go with the T105, I will have to use it due to space. With fewer L16s, I will have full easy access to the tops of the batts

Based on SV Alchemy's suggestion, I am looking seriously at the L16 size, just a bit more $$ and I suspect a much better battery and I can use fewer of them = less cabling. I do have wind (not yet installed) and since I am a cat, I must motor all the time as per the other thread so will pick up some from the alternator. We lived completely on 270 watts of solar last time and a smaller 359 AH battery bank ( 6-7 year old gel cells)

Also per Alchemy's suggestion, will be fabricating a better battery box but the 120 # L16 will take more than me to lift into position.
Hey Ed,

It sounds like you are well on your way to a perfect and robust solution for your needs. And you make a good point about the cabling...

Kudos!

Bill
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is offline   Reply With Quote
Old 09-12-2015, 12:30   #14
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,678
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Quote:
Originally Posted by nigel1 View Post
Regarding the Hydrolink system, I have just fitted this to 6 Trojan batteries, and am impressed with the system, easy to fit and looks good quality.
Because two of my batteries are in a separate location I need to modify the system a bit and needed a second coupler. As Trojan only sell the whole kit, the coupler was purchased from
https://flow-rite.com/
at a reasonable price.
Hi Nigel,

I like the Hydrolink system also. It made my expanded house bank possible...

Thanks for the reference to acquire bits and pieces for the system from Flow-Rite.

Cheers!

Bill
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is offline   Reply With Quote
Old 09-12-2015, 18:29   #15
Registered User

Join Date: Feb 2006
Location: Eastern Caribbean for the 2020 season then east coast or Panama
Boat: Lagoon 470 cat
Posts: 699
Re: 6 T-105 OR 4 TROJAN J305E-AC?

Little bit of 2 cents worth here regarding solar sizing. I would not bother limiting the solar based on the battery capacity. There are some items (watermakers, ice makers, freezers, even our washing machine, etc.) that are nice to run during the day using "excess" solar capacity. Always nice to have the batteries in float mode by noon. Little extra cost for the panels, but in my case the extra juice is usually put to good use.

That being said, I am assuming that the solar controller is 3 stage so it will not burn up the batteries. Would think all "modern" ones are.

Bill
Moontide is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Determining the age of Trojan T-105's unbusted67 Electrical: Batteries, Generators & Solar 5 24-06-2014 06:04
Trojan T-105's versus Crowns LBW399 Electrical: Batteries, Generators & Solar 17 29-12-2013 20:04
Trojan T-105 6v Batteries VirtualVagabond Electrical: Batteries, Generators & Solar 35 09-06-2013 20:44
Trojan t-105 in So. Cal Thermal Electrical: Batteries, Generators & Solar 0 06-12-2007 21:54
Source for Trojan T-105 in Palm Beach or alternative battery svAlegria Electrical: Batteries, Generators & Solar 2 19-03-2007 13:46

Advertise Here


All times are GMT -7. The time now is 17:15.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.