3 50 watt solar panels producing 1.9 amps

My charge controller is showing that my 3 50 watt solar panels are only producing 1.9 amps? Panels are 24 volt panels by Sunware. My batteries are 24 volt.

Isn't this a low output? My controller is not a Mppt type? Would that help?
__________________

dm567 is offline   Reply With Quote
Old 26-03-2017, 16:55   #2
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 5,874
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by dm567 View Post
My charge controller is showing that my 3 50 watt solar panels are only producing 1.9 amps? Panels are 24 volt panels by Sunware. My batteries are 24 volt.

Isn't this a low output? My controller is not a Mppt type? Would that help?
More data please.

  • Open circuit voltage
  • MPP voltage
  • Charge controller type
  • You are sure it is a 24v system?
If the open circuit voltage is 24v, the MPP is probably around 18-19V and you are going to need a booster, not just a MPPT controller. Either that or the panels need to be re-wired in series, depending on the MPPT controller capabilities.

More data.
__________________

__________________
Gear Testing--Engineering--Sailing
http://sail-delmarva.blogspot.com/
thinwater is offline   Reply With Quote
Old 26-03-2017, 17:30   #3
Registered User

Join Date: Jan 2013
Location: Lake Macquarie, NSW, Australia
Boat: Beneteau, Oceanis, 34
Posts: 41
Re: 3 50 watt solar panels producing 1.9 amps

More date will be helpful. That said, u would bet it's voltage drop. Too long a cable at too small a diameter and you'll lose amps. Always my first guess.
capblasters is offline   Reply With Quote
Old 26-03-2017, 18:30   #4
Registered User

Join Date: May 2013
Posts: 4
Re: 3 50 watt solar panels producing 1.9 amps

I'm new to this. Voltage is higher than 24 volts. I meant that I have 24 volt batteries. I'll measure voltage from the 3 panels and post. I'm away from boat right now for a few weeks

So I should measure open voltage from panels by dissconnecting each one from the controller and measuring voltage, right?

How do I measure Mpp voltage?

Controller is a photos cml10. It is not mppt


Thanks for getting me started
dm567 is offline   Reply With Quote
Old 26-03-2017, 19:30   #5
Bailing as fast as I can.
 
GILow's Avatar

Join Date: Sep 2008
Location: Adelaide, South Australia
Boat: Swanson 42
Posts: 4,368
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by dm567 View Post
...
Controller is a photos cml10. It is not mppt
I think that got auto-corrected.. probably a phocos cml10.


Quote:
Originally Posted by dm567 View Post
I'm new to this. Voltage is higher than 24 volts. I meant that I have 24 volt batteries.
My sincere apologies if this is obvious to you, but it may not be obvious to everyone... there's no chance you have two 12 volt batteries in parallel is there? That might look like 24 volts but be providing 12 volts? The reason I ask is that 24 volt systems are a little rare and usually used on large battery systems. Normally I would expect to see very large solar arrays connected to them (a few kilowatts) not a few 50 watt panels.
__________________
Have you heard the news? Esmeralda is OK.

I had resolved on a voyage around the world, and as the wind on the morning of April 24, 1895 was fair, at noon I weighed anchor....
GILow is offline   Reply With Quote
Old 26-03-2017, 19:31   #6
Bailing as fast as I can.
 
GILow's Avatar

Join Date: Sep 2008
Location: Adelaide, South Australia
Boat: Swanson 42
Posts: 4,368
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by capblasters View Post
More date will be helpful. That said, u would bet it's voltage drop. Too long a cable at too small a diameter and you'll lose amps. Always my first guess.
Hmmm... sounds like you've been bitten by this one too hey?
__________________
Have you heard the news? Esmeralda is OK.

I had resolved on a voyage around the world, and as the wind on the morning of April 24, 1895 was fair, at noon I weighed anchor....
GILow is offline   Reply With Quote
Old 26-03-2017, 19:44   #7
Marine service provider
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 6,280
Re: 3 50 watt solar panels producing 1.9 amps

My first question would be are you sure that your panels are 24 volt panels?
They would show extremely low if they are 12 v panels hooked into a 24v battery bank.
We really need lots more information.
__________________
Non illigitamus carborundum
newhaul is online now   Reply With Quote
Old 26-03-2017, 20:19   #8
Senior Cruiser

Cruisers Forum Supporter

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 6,707
Re: 3 50 watt solar panels producing 1.9 amps

You don't mention the charge state of the batteries. Full batteries won't take high amperage.
__________________
Paul
Paul L is online now   Reply With Quote
Old 26-03-2017, 20:24   #9
Senior Cruiser
 
StuM's Avatar

Cruisers Forum Supporter

Join Date: Nov 2013
Location: Port Moresby,Papua New Guinea
Boat: FP Belize Maestro 43
Posts: 8,139
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by dm567 View Post
I'm new to this. Voltage is higher than 24 volts. I meant that I have 24 volt batteries. I'll measure voltage from the 3 panels and post. I'm away from boat right now for a few weeks

So I should measure open voltage from panels by dissconnecting each one from the controller and measuring voltage, right?

How do I measure Mpp voltage?

Controller is a photos cml10. It is not mppt


Thanks for getting me started
You said that your charge controller is showing 1.9 Amps. The Phocos CML10 doesn't have a display to show current, so where are you seeing the 1.9 Amp displayed?



How many and what brand/model batteries do you have (and are they connected in series of parallel) ?

What was the SOC/battery voltage when you measured 1.9A and what latitude and time of day?

What loads were on the system at the time?
StuM is online now   Reply With Quote
Old 27-03-2017, 02:03   #10
Registered User
 
Viking Sailor's Avatar

Join Date: Nov 2006
Location: San Francisco Bay
Boat: Fantasia 35
Posts: 1,176
Re: 3 50 watt solar panels producing 1.9 amps

24 volts times 1.9 amps equals 45.6 watts. This power is about what one expects out of a 50 watt panel operating at about 90% efficiency. Could it be that you have only one panel connected to the controller, or have only one functioning panel?
Viking Sailor is offline   Reply With Quote
Old 27-03-2017, 10:36   #11
Registered User
 
SouthernPride's Avatar

Join Date: Aug 2015
Location: Charleston, SC
Boat: 53' Hatteras Cruising Yacht
Posts: 172
Re: 3 50 watt solar panels producing 1.9 amps

Wired incorrectly
SouthernPride is offline   Reply With Quote
Old 27-03-2017, 10:55   #12
Registered User
 
Privilege's Avatar

Join Date: Oct 2009
Location: Bermuda
Boat: Privilege 435
Posts: 523
Images: 12
Re: 3 50 watt solar panels producing 1.9 amps

I'm with Paul; if your batteries are fully charged, or almost charged, they are not going to accept more than a few amps no matter how much the panels want to give them.
Privilege is offline   Reply With Quote
Old 27-03-2017, 11:37   #13
Registered User

Join Date: Apr 2013
Location: So Cal
Boat: Catalina 30
Posts: 953
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by StuM View Post
You said that your charge controller is showing 1.9 Amps. The Phocos CML10 doesn't have a display to show current, so where are you seeing the 1.9 Amp displayed?
Phocos has an optional remote display:


I'd guess 12v batteries, possibly the solar is wired incorrectly. Noone can know unless the OP posts back with much more detail.
jeepbluetj is offline   Reply With Quote
Old 30-03-2017, 21:59   #14
Registered User

Join Date: May 2013
Posts: 4
Re: 3 50 watt solar panels producing 1.9 amps

This Farr 50 pilothouse is from Europe and it does have a large 24 volt battery bank. The panels are listed as 24 volt panels from the manufacturers website and produce more than 24 volts. Yes, I thought the size of the panels were quite small, but I'm hoping they will at least keep the batteries full while I'm away should something happen to the shore power.

Yes I have the optional Phocos display and it was reading 1.9 amps. The batteries were full. I will test again with the batteries partially drained. It's a different model than the the one pictured but basically the same. I don't know if it reads the amps from the panels or to the batteries. It does have a switch and I set to the picture of the panel with amps written below it so I though it was amps from the panels. What happens to extra power generated that doesn't go to the batteries? I've never seen the controller hot and its small and I can't see any heat sinks?

I will retest every thing based on your comments when I drive down to the boat. It's in Enscenada Mexico.

Thank you for all the input.

I will post again when I get down there. I live in San Francisco.
dm567 is offline   Reply With Quote
Old 31-03-2017, 00:56   #15
Senior Cruiser
 
StuM's Avatar

Cruisers Forum Supporter

Join Date: Nov 2013
Location: Port Moresby,Papua New Guinea
Boat: FP Belize Maestro 43
Posts: 8,139
Re: 3 50 watt solar panels producing 1.9 amps

Quote:
Originally Posted by dm567 View Post
This Farr 50 pilothouse is from Europe and it does have a large 24 volt battery bank. The panels are listed as 24 volt panels from the manufacturers website and produce more than 24 volts. Yes, I thought the size of the panels were quite small, but I'm hoping they will at least keep the batteries full while I'm away should something happen to the shore power.

Yes I have the optional Phocos display and it was reading 1.9 amps. The batteries were full. I will test again with the batteries partially drained. .
Suggest you read up on lead acid battery charging. As batteries approach 100% State of Charge(SOC), their ability to accept charge at the set "absorption voltage" or "float voltage" decreases to zero or close to it. You can't tell anything about the efficiency of your solar system when your batteries are fully charged.
__________________

StuM is online now   Reply With Quote
Reply

Tags
panels, solar, solar panels

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Amps v Amp hours v Amps/Hr StuM Electrical: Batteries, Generators & Solar 255 25-01-2016 14:21
85 Watt Solar Panels - Where to Buy ? SV Demeter Electrical: Batteries, Generators & Solar 7 06-07-2011 15:39
How to Set Up 3 x 130w 12vdc Solar Panels for 24vdc with the Most Amps ? Fuss Electrical: Batteries, Generators & Solar 3 06-04-2010 00:25
30+ amps from solar panels! schoonerdog Electrical: Batteries, Generators & Solar 34 17-07-2008 23:21
FS: (2) 85 watt Kryocera Solar Panels benjiwoodboat Classifieds Archive 15 30-10-2007 07:26



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 20:07.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.