12V Relay Amp Ratings?

Looking at some typical twelve volt power relays, similar to the common Bosch "30A" 12v spdt type, I see that a lot of them are no longer rated with just one amp rating. Instead, they typically are rated "50A/30A" or "40A/20A" and one maker (NTE) explains that as "50A for the NO contacts, 30A for the NC contacts". Hella rates the same way, these are not nameless brands.

So in other words, the relay contacts are asymmetric now, and the contact for the NC position is not rated anywhere near what the NO position is rated for. Which just seems plain foolish to me, especially since so many of them are advertised JUST by the larger NO rating, which is not the rating they'd normally be used in service for.

Did I miss the memo? Have standards always called for this or are the makers just cheaping out and playing ratings inflation now?

Waiter, my reality check please?
__________________

__________________
hellosailor is offline   Reply With Quote
Old 24-07-2013, 13:46   #2
Do… or do not
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 9,198
I believe the higher rating is for making contact and the lower rating is for braking contact. At least, that is how we designed circuits around them; I had little patience with these half mechanical devices with springs and stuff.

EDIT: you get arcing when opening contacts much sooner then when closing contacts.
__________________

__________________
s/v Jedi is offline   Reply With Quote
Old 24-07-2013, 14:05   #3
֍֎֍֎֍֎֍֎֍֎

Cruisers Forum Supporter

Join Date: Apr 2006
Posts: 13,056
Re: 12V relay amp ratings?

Nick, NTE was very specific about this. Theirs are not make/break ratings, but separate ratings for the NO/vs/NC contacts. Which seems ludicrous to me but in this day and age, when a gallon contains 56 ounces and a pound of coffee only 10.5-12 ounces...I'm used to that.

Make/break ratings, AC vs DC, arcing, all these things are nice but apparently this is something else they are doing.
__________________
hellosailor is offline   Reply With Quote
Old 24-07-2013, 16:34   #4
Registered User
 
Viking Sailor's Avatar

Join Date: Nov 2006
Location: San Francisco Bay
Boat: Fantasia 35 - s/v Feeling Good
Posts: 1,074
Re: 12V relay amp ratings?

Just guessing here... But since a SPDT relay is often used as a SPST relay it might make sense to have the NO contact be designed to carry the larger current. It seem less likely that someone would want to supply high current continuously through a relay in a 12V system. That level of current seem more suited to a solenoid.
__________________
Viking Sailor is offline   Reply With Quote
Old 24-07-2013, 17:00   #5
֍֎֍֎֍֎֍֎֍֎

Cruisers Forum Supporter

Join Date: Apr 2006
Posts: 13,056
Re: 12V relay amp ratings?

That would make sense, but then why not save a penny more and just sell it as an SPST relay? Why skimp on just the one contact?? Heck, cut out the contact and the qd fitting and you can even save two cents on each relay. Maybe three.

How many accountants do you have to keelhaul before they rub all the barnacles off a hull anyhow??
__________________
hellosailor is offline   Reply With Quote
Old 24-07-2013, 17:47   #6
Registered User
 
Viking Sailor's Avatar

Join Date: Nov 2006
Location: San Francisco Bay
Boat: Fantasia 35 - s/v Feeling Good
Posts: 1,074
Re: 12V relay amp ratings?

Maybe it is just cheaper to make, package, stock, and distribute a standard product at a higher cost to the user then to do the same for two standard products. The rating difference could be the result of upgrading an old product to meet new requirements at the lowest possible cost. Again, this guessing.
__________________
Viking Sailor is offline   Reply With Quote
Old 25-07-2013, 07:43   #7
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: 12V Relay Amp Ratings?

It is nothing new. Most SPDT relays have a spring return that holds the NC contact closed and a solenoid to pull the armature and contact to close the NO side. There has to be enough magnetic force to overcome the spring when it first turns on but once the armature seats closed there is 10 times as much force than is needed so greater pressure on the NormallyOpen contact than is provided by just the spring on the NormallyClosed giving a higher current capacity for the NO contact.

In fact you can reduce the current in the coil by as much as 80% once the contact is closed to reduce power consumption and heating. Some of our larger Combiners have this feature although the smaller ones only use about 1 to 2 watts so there is little to gain for the extra controls.
__________________
Andina Marie is offline   Reply With Quote
Old 25-07-2013, 16:47   #8
Nearly an old salt
 
goboatingnow's Avatar

Cruisers Forum Supporter

Join Date: Jun 2009
Posts: 13,649
Images: 3
NC contacts are almost invariably rated lower then NO. this is because destructive arcing occurs when the contact starts opening not when it starts closing. ( ie inductive effects. )
Dave
__________________
Check out my new blog on smart boat technology, networking and gadgets for the connected sailor! - http://smartboats.tumblr.com
goboatingnow is offline   Reply With Quote
Old 25-07-2013, 18:02   #9
֍֎֍֎֍֎֍֎֍֎

Cruisers Forum Supporter

Join Date: Apr 2006
Posts: 13,056
Re: 12V Relay Amp Ratings?

Thanks, Andina, and Dave.

That makes sense. If I'm reading between the lines correctly, the actual contacts are the same then, but one is derated because it will see more severe conditions even though it is physically the same part. So they're not cheating on the parts, but the ratings are recognizing that one will be more severely stressed and should be treated more kindly.

Yes?

As it turns out I am using the relay as SPST anyway, so the lower rating for the unused contact won't matter in this application. Nice to know and understand for the future though.

Ah, for the old days an mercury-wetted relays.<G>
__________________
hellosailor is offline   Reply With Quote
Old 25-07-2013, 21:52   #10
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: 12V Relay Amp Ratings?

Quote:
Originally Posted by goboatingnow View Post
NC contacts are almost invariably rated lower then NO. this is because destructive arcing occurs when the contact starts opening not when it starts closing. ( ie inductive effects. )
Dave
No, both the NO and the NC contacts both close and open their respective circuits. The amount of arcing is a function of the circuit parameters, not which contact is being used.

The lower rating of the NC contact is due to the lower mechanical contact pressure from the spring return compared to the magnetic force on the NO contact.
__________________
Andina Marie is offline   Reply With Quote
Old 26-07-2013, 03:02   #11
Do… or do not
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 9,198
Quote:
Originally Posted by Andina Marie View Post
No, both the NO and the NC contacts both close and open their respective circuits. The amount of arcing is a function of the circuit parameters, not which contact is being used.

The lower rating of the NC contact is due to the lower mechanical contact pressure from the spring return compared to the magnetic force on the NO contact.
That must be it. The other option of arcing on opening was the first thing I had mentioned already but manufacturers said the contact itself. With contacts being the same normally, it must indeed be the force in each direction that differs.... but I haven't worked out which way yet...

EDIT: the NO opens with the spring while the NC opens with the magnet. That would make the NC quicker and stronger in opening, not the NO. But.. the NO using the magnet, has the spring working against it, which must be overcome with the magnet.

I'm pretty sure we must look at opening of contacts for maximum ratings, not the closing of contacts.
__________________
s/v Jedi is offline   Reply With Quote
Old 26-07-2013, 03:31   #12
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 4,028
NO uses the magnet to close and therefore has higher contact pressure thus higher current rating.
__________________
transmitterdan is offline   Reply With Quote
Old 26-07-2013, 06:51   #13
Do… or do not
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 9,198
Quote:
Originally Posted by transmitterdan View Post
NO uses the magnet to close and therefore has higher contact pressure thus higher current rating.
I don't agree. When NO or NC cntacts are closed, they can transfer many times the current that they are rated for. It is when they must make or break that circuit that is critical. To open cntacts when max. Current is flowing is the big problem for the contact; this is the moment they burn.
__________________
s/v Jedi is offline   Reply With Quote
Old 26-07-2013, 09:37   #14
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: 12V Relay Amp Ratings?

Quote:
Originally Posted by s/v Jedi View Post
I don't agree. When NO or NC cntacts are closed, they can transfer many times the current that they are rated for. It is when they must make or break that circuit that is critical. To open cntacts when max. Current is flowing is the big problem for the contact; this is the moment they burn.
Jedi, both the NO contact and the NC contact have to make and break current.
Perhaps you misunderstand the NO and NC meaning.
The NC contact is closed when there is no power on the relay coil, it connects the armature to the NC terminal but although the relay is idle this contact is closed and can carry current.

The NO contact is closed when power is applied to the coil. That breaks the NC connection and closes the NO contact.

Both have closing functions which can involve heavy current.
BOTH HAVE opening functions that can cause arcing.
If the current is the same, both have identical problems with inrush current and arcing.
In fact if you get down to the nitti gritti when a NO contact closes it does so with higher power than the return spring of a NC contact so the extra speed and acceleration at the last moment causes much more contact bounce that you see at the gentler closing of a NC contact closing. This means breaking the inrush current and arcing a number of times on the NO contact.

As I've indicated previously, in over 20 years we have never had a Combiner relay contact failure.

One fishing boat who had been using our old 150 amp Combiner complained that his Combiner had always BUZZED when the batteries were around 13.2 volts and that was annoying. It had been running for 5 years with the timing capacitor not functioning so instead of limiting operation to 1 per minute it was doing 10 per second. So 5 years running was the equivalent of 3,000 years normal use. He sent it back and the relay contacts were about 50% eroded. I put in a new timing capacitor and returned it to him, should be good for at least another 2,000 years .
__________________
Andina Marie is offline   Reply With Quote
Old 26-07-2013, 13:29   #15
Do… or do not
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 9,198
Quote:
Originally Posted by Andina Marie View Post
Jedi, both the NO contact and the NC contact have to make and break current.
Perhaps you misunderstand the NO and NC meaning.
The NC contact is closed when there is no power on the relay coil, it connects the armature to the NC terminal but although the relay is idle this contact is closed and can carry current.

The NO contact is closed when power is applied to the coil. That breaks the NC connection and closes the NO contact.

Both have closing functions which can involve heavy current.
BOTH HAVE opening functions that can cause arcing.
If the current is the same, both have identical problems with inrush current and arcing.
In fact if you get down to the nitti gritti when a NO contact closes it does so with higher power than the return spring of a NC contact so the extra speed and acceleration at the last moment causes much more contact bounce that you see at the gentler closing of a NC contact closing. This means breaking the inrush current and arcing a number of times on the NO contact.

As I've indicated previously, in over 20 years we have never had a Combiner relay contact failure.

One fishing boat who had been using our old 150 amp Combiner complained that his Combiner had always BUZZED when the batteries were around 13.2 volts and that was annoying. It had been running for 5 years with the timing capacitor not functioning so instead of limiting operation to 1 per minute it was doing 10 per second. So 5 years running was the equivalent of 3,000 years normal use. He sent it back and the relay contacts were about 50% eroded. I put in a new timing capacitor and returned it to him, should be good for at least another 2,000 years .
Andina, no need to explain me NO vs NC, I am a retired electronics designer. But I could need an explanation why NO gets a higher rating. Like I wrote a number of times already, I think that opening of the contact (any contact) while it is carrying max. rated current (i.e. arcing), is the limiting factor for it's rating, followed by closing of contacts. This is why I only look at what happens when a contact opens. Pls. Explain why when you do not agree with that.
__________________

__________________
s/v Jedi is offline   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Electrical Distribution Panel 50 amp Azzurra Classifieds Archive 6 02-04-2013 11:45
36 Volt Solar Panel , 250 watts - Can I Connect to 12V Solar Regulator ? surfmachine Electrical: Batteries, Generators & Solar 53 19-04-2012 18:32
Airconditioning Raw Water Pump Relay Box Capt. Rich Plumbing Systems and Fixtures 3 06-01-2012 09:14
Three-Prong Oil Pressure Switch and Electric Fuel Pump - Is a Fuel Pump Relay Needed? sdowney717 Electrical: Batteries, Generators & Solar 4 29-09-2011 08:06
Windlass Relay Control Box Problem hoppy Anchoring & Mooring 3 26-09-2011 01:39



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 03:39.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.