Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 18-04-2015, 17:48   #1
Registered User

Join Date: Apr 2015
Posts: 2
Passport II marine air

I bought a 1995 cruiser last fall and had a dealer of this make go over it entirely. Everything seems to work well, including this AC unit. However, I tried using the heat setting in cool spring weather, and while the control panel indicated it was in heat mode, and the thermostat was set at 85, I never got any heat out of it. Does this model include heat, or has anyone else experienced a similar problem with this brand of unit?
Moondog is offline   Reply With Quote
Old 18-04-2015, 18:09   #2
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Passport II marine air

Post model number please
redsky49 is offline   Reply With Quote
Old 18-04-2015, 19:08   #3
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Passport II marine air

Here's a link to the manual hope it helps you some Passport II Manual I have no personal experience with the units
newhaul is offline   Reply With Quote
Old 19-04-2015, 03:54   #4
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,439
Images: 241
Re: Passport II marine air

Greetings and welcome aboard the CF, Moondog.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 19-04-2015, 06:03   #5
Registered User
 
S/V Illusion's Avatar

Join Date: Oct 2007
Location: Lakewood Ranch, FLORIDA
Boat: Alden 50, Sarasota, Florida
Posts: 3,472
Re: Passport II marine air

"Cool spring weather" doesn't indicate the water temperature. As this is a heat pump, you can only extract heat from water above a certain temperature. As you don't specify the water temp, it's not possible for anyone here to know the efficacy of a heat pump system.
S/V Illusion is offline   Reply With Quote
Old 19-04-2015, 06:16   #6
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Passport II marine air

If it is a "reverse cycle" AC, (reverses from cooling to heating), there is a valve that is known for sticking. The common solution is to tap the valve with the handle of a screwdriver to free it.

The trick is knowing where the valve is, how big a screwdriver to use and how hard to tap it. A pair of pliers would work as well.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 19-04-2015, 06:53   #7
Registered User

Join Date: Apr 2015
Posts: 2
Re: Passport II marine air

Thanks guys for all your help. The only information I could find on the unit or in the manual is that it is called a passport II model. I could not find a specific model number although I'm sure there's one that exists. The boat is in Kentucky, so I'm sure the water temperatures are probably in the fifties right now and if it is a heat pump system perhaps water is not warm enough to create any heat. I even asked the dealer if the hot water heater had anything to do with it and they said no. I will look for the reversing valve because there was some suggestion in the manual that some of the models use a reversing system. You've given me some good ideas.
Moondog is offline   Reply With Quote
Old 19-04-2015, 07:00   #8
Registered User
 
Catnut's Avatar

Join Date: May 2011
Location: Montpellier, France
Boat: FP Bahia 46 catamaran
Posts: 34
Re: Passport II marine air

I have just had the same problem. There is reversing valve that sometimes sticks, driven by a solenoid. I tried tapping the valve with a long handled screw driver, but it still stayed in cooling mode.
I removed the solenoid, tested it, and found that it had gone open circuit. Replacing the solenoid, as a temporary fix with a similar but not identical one, fixed it for us for the time being.

Tony
Catnut is offline   Reply With Quote
Old 19-04-2015, 11:08   #9
Registered User

Join Date: Dec 2011
Location: Rockland Harbor, ME
Boat: Triangle 32, center-cockpit ketch
Posts: 40
Re: Passport II marine air

One comment on the function of heat pumps. There's a misconception that the source (air or water) of heating and cooling must be warm (heating) or cold (cooling) in order for the units to function. Not true. Air-source heat pumps will heat a house to a comfortable level with an air temperature of -15 F, and will cool the house at outside temperatures of +95 F. Not as efficiently as at more moderate source temperatures, but they'll do it.
Water-source heat pumps should work just fine as long as the water is pumpable -ie. not frozen. That's 32 F in fresh water and 26 F or so in salt.
kjdavie01 is offline   Reply With Quote
Old 19-04-2015, 17:08   #10
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Passport II marine air

Quote:
Originally Posted by kjdavie01 View Post
One comment on the function of heat pumps. There's a misconception that the source (air or water) of heating and cooling must be warm (heating) or cold (cooling) in order for the units to function. Not true. Air-source heat pumps will heat a house to a comfortable level with an air temperature of -15 F, and will cool the house at outside temperatures of +95 F. Not as efficiently as at more moderate source temperatures, but they'll do it.
Water-source heat pumps should work just fine as long as the water is pumpable -ie. not frozen. That's 32 F in fresh water and 26 F or so in salt.
While correct in theory, in practical terms air source heat pumps begin to lose the battle when heating around 20F. The COP, or measurement of heating performance of a heat pump, is based on 47F outside air temperature. At that temperature a heat pump may have a COP of 3.0 or better which means it is producing three times the heat output as compared to traditional resistance heaters. As outside air temperatures drop, so does the efficiency of the unit. Correspondingly, the discharge or supply air temperature will also drop, frequently to the point that the room temperature setpoint can no longer be maintained. User complaints regarding this dropping of the discharge air temperature ( often less than 80 degrees) are the number one complaint, despite whether the unit can maintain setpoint. The air coming out of the unit feels cold. It is for this reason that domestic heat pumps have an auxiliary or emergency heat setting to energize the supplemental resistance heat.

What the OP might be experiencing is this exact condition. Being a water source unit, the seawater temperature has a direct bearing on the outlet temperature. The unit could be in the heating mode but discharging only moderately warm air.

I would also suggest that the evaporator filter, often on the back of the unit, be vacuum cleaned. I often find that these filters are never cleaned, which leads to numerous problems.
redsky49 is offline   Reply With Quote
Old 20-04-2015, 09:31   #11
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,438
Re: Passport II marine air

Quote:
Originally Posted by Moondog View Post
Thanks guys for all your help. The only information I could find on the unit or in the manual is that it is called a passport II model. I could not find a specific model number although I'm sure there's one that exists. The boat is in Kentucky, so I'm sure the water temperatures are probably in the fifties right now and if it is a heat pump system perhaps water is not warm enough to create any heat. I even asked the dealer if the hot water heater had anything to do with it and they said no. I will look for the reversing valve because there was some suggestion in the manual that some of the models use a reversing system. You've given me some good ideas.

Passport II is the nomenclature for the control panel system. A more modern one is the Elite control panel, etc. and that ads some programmable features.

Not sure what the actual reverse cycle unit nomenclature is... and I'm here, and docs are there. (And if I remember right, the "manual" isn't all that informative, except for installation instructions.)

Anyway, that's the system we have.... and yes, it's supposed to put out heat if the reversing valve is working. Not to be confused with an additional resistive coil arrangement that could have been fitted on some systems, too. Give no heat output, you likely don't have that resistive addition anyway.

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 20-04-2015, 10:35   #12
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Passport II marine air

A way to determine if the reversing valve is functioning is to change from cooling to heating mode when the unit is operating, if the valve functions, there should be a loud "whoosh" noise when it functions.
I want to think that around 50 deg water temp is about where a marine heat pump loses it's capability to produce much heat, to some extend the amount of water flow through the system also contributes, so if the strainer is partially blocked, you lose efficiency there too.
a64pilot is offline   Reply With Quote
Old 20-04-2015, 10:42   #13
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Passport II marine air

Quote:
Originally Posted by ranger42c View Post
Passport II is the nomenclature for the control panel system. ...............
True. The information for the air conditioner would be on the air conditioner itself.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 20-04-2015, 11:42   #14
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Passport II marine air

A unit capable of heating (and not all are by the way) would either have an electric resistance coil or would have a "reversing" valve in lieu of a typical thermostatic expansion valve. The ability to both heat and cool utilizing a compression cycle makes it a 'heat pump'.

If you can determine the amperage being used, either by a panel mounted ammeter or a multimeter, the first thing I would check is if the amperage increases when you go from the 'FAN' position to the 'HEAT' position. There should be a big leap of from 6 to 12 amps over fan only,typically.

Having a control panel that shows a heat position is encouraging but not definitive. What exactly did the refrigeration rep do while examining your unit? Or were you referring in post #1 to the rep for the boat manufacturer?
redsky49 is offline   Reply With Quote
Old 20-04-2015, 11:48   #15
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Passport II marine air

Quote:
Originally Posted by a64pilot View Post
A way to determine if the reversing valve is functioning is to change from cooling to heating mode when the unit is operating, if the valve functions, there should be a loud "whoosh" noise when it functions.
I want to think that around 50 deg water temp is about where a marine heat pump loses it's capability to produce much heat, to some extend the amount of water flow through the system also contributes, so if the strainer is partially blocked, you lose efficiency there too.
Generally, if the strainer is blocked the unit will go off due to high head pressure, or perhaps trip the breaker.

I will admit that I am not a marine HVAC technician, though I am a retired Mechanical Engineer, so take my comments with some caution.

I would also take some accurate temperature measurements, incoming/return air and outgoing/supply air and note the delta.
redsky49 is offline   Reply With Quote
Reply

Tags
marine


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Marine air passport control problem or not? Capt.Alex Plumbing Systems and Fixtures 0 03-09-2013 13:54

Advertise Here


All times are GMT -7. The time now is 22:20.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.