Old 01-03-2018, 21:36   #1
Registered User

Join Date: Apr 2017
Location: Guam
Boat: Kings Legend 41
Posts: 9
Using low-voltage water heating elements as a diversion load.

Has anyone tried retrofitting a 120/240 VAC hot water tank with a DC element? I'm re-designing my solar system and adding a wind generator. Rather than shunting excess I think a better diversion would be heating water. Just curious if anyone else has tried it..
__________________
Austin & Belinda
SV Flying Spirit
Kings Legend 41
SV FlyingSpirit is offline   Reply With Quote
Old 02-03-2018, 04:49   #2
Registered User
 
deblen's Avatar

Join Date: Oct 2014
Location: Bay of Fundy,Grand Manan,N.B.,Canada N44.40 W66.50
Boat: Mascot 28 pilothouse motorsailer 28ft
Posts: 3,253
Images: 1
Re: Using low-voltage water heating elements as a diversion load.

You can dump your excess solar panel current into a 120/240 heater element.
Voltage rating of element doesn't matter.
However! You can't tie your solar panel DC into the same element that is being fed 120/240,without using a "transfer" switch/relay.

Len

Click image for larger version

Name:	Ohms Law.jpg
Views:	334
Size:	172.3 KB
ID:	165225



Name:   ohmchart.gif
Views: 1234
Size:  3.1 KB
__________________
My personal experience & humble opinions-feel free to ignore both
.
deblen is offline   Reply With Quote
Old 02-03-2018, 05:30   #3
Registered User
 
TreblePlink's Avatar

Join Date: Aug 2017
Location: Kentucky
Boat: 1969 Rhodes 28'
Posts: 307
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by deblen View Post
You can dump your excess solar panel current into a 120/240 heater element. Voltage rating of element doesn't matter.
[...]
Except that the 120 vac heating element won't draw much current at 12 volts, and won't heat much.

I would replace with 12 volt elements; but remember that all electrical heating takes lots of energy.
TreblePlink is offline   Reply With Quote
Old 02-03-2018, 05:31   #4
Registered User

Join Date: Apr 2013
Location: Penobscot Bay, Maine
Boat: Tayana 47
Posts: 2,123
Re: Using low-voltage water heating elements as a diversion load.

There's a dual AC/DC hot water heater element available to do just what you are thinking about and it was installed in my water heater when I bought my current boat. Unless you're located someplace like the Caribbean I doubt that you'll spend much time with your batteries fully charged so any current is available to for your dump load. Even then, not too many cruisers report having amps to spare very often. Also, the AC element that's included in the dual element I had was such low power that it took at least an hour of running the generator just to get my water heater up to temp and now that I have a "normal" AC element it takes about 20 minutes. The only way I'd go with such an arrangement again would be if the hot water tank had two separate places to install heating elements so my ability to use AC power would not be degraded like it was with the dual element.
jtsailjt is offline   Reply With Quote
Old 02-03-2018, 05:48   #5
Registered User
 
deblen's Avatar

Join Date: Oct 2014
Location: Bay of Fundy,Grand Manan,N.B.,Canada N44.40 W66.50
Boat: Mascot 28 pilothouse motorsailer 28ft
Posts: 3,253
Images: 1
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by TreblePlink View Post
Except that the 120 vac heating element won't draw much current at 12 volts, and won't heat much.

I would replace with 12 volt elements; but remember that all electrical heating takes lots of energy.
You are correct that the 120vac element "won't draw much current".

In fact it will only draw 1/10 the amps current as a 12V element would draw.

But due to ohm's law,both elements will produce the same wattage,& therefore,the same heat into the water.

Len
__________________
My personal experience & humble opinions-feel free to ignore both
.
deblen is offline   Reply With Quote
Old 02-03-2018, 06:15   #6
Registered User
 
TreblePlink's Avatar

Join Date: Aug 2017
Location: Kentucky
Boat: 1969 Rhodes 28'
Posts: 307
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by deblen View Post
You are correct that the 120vac element "won't draw much current".

In fact it will only draw 1/10 the amps current as a 12V element would draw.

But due to ohm's law,both elements will produce the same wattage,& therefore,the same heat into the water.

Len
Huh? I realize that heating elements change resistance a bit with temperature, but not THAT much. Here is the simple math:

10 Ohm element: with 120 volts RMS: 12 amperes. times 120 volts,
= 1440 watts.


10 Ohm element: with 12.6 volts DC 1.26 amperes. times 12.6 volts
= 15 watts.

Chris
TreblePlink is offline   Reply With Quote
Old 02-03-2018, 07:13   #7
Registered User
 
TreblePlink's Avatar

Join Date: Aug 2017
Location: Kentucky
Boat: 1969 Rhodes 28'
Posts: 307
Re: Using low-voltage water heating elements as a diversion load.

Somewhere along the way,

"You can dump your excess solar panel current into a 120/240 heater element. Voltage rating of element doesn't matter."

(using the original 120 volt element at 12 volts)


Morphed into:

"both elements" (another, different element?)

TreblePlink is offline   Reply With Quote
Old 02-03-2018, 07:40   #8
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 736
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by deblen View Post
You are correct that the 120vac element "won't draw much current".

In fact it will only draw 1/10 the amps current as a 12V element would draw.

But due to ohm's law,both elements will produce the same wattage,& therefore,the same heat into the water.

Len
That's interesting, less current and less votage, yet the same power ... Can you show your calculation ?
rom is offline   Reply With Quote
Old 02-03-2018, 08:18   #9
Registered User

Join Date: Sep 2007
Location: Delray Beach, Fl
Boat: 1998 Rosborough 246 LSV
Posts: 563
Re: Using low-voltage water heating elements as a diversion load.

I dumped excess solar into a water maker. Same idea
captstu is offline   Reply With Quote
Old 02-03-2018, 08:27   #10
Registered User

Join Date: Apr 2013
Location: Penobscot Bay, Maine
Boat: Tayana 47
Posts: 2,123
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by TreblePlink View Post
Somewhere along the way,

"You can dump your excess solar panel current into a 120/240 heater element. Voltage rating of element doesn't matter."

(using the original 120 volt element at 12 volts)


Morphed into:

"both elements" (another, different element?)

I was the one who mentioned the 2 separate elements. The reason being that I think it's a VERY bad idea to connect AC and DC systems through a hot water heater, even if you have a switch to only have one connection live at a time. And if you don't have switches to keep only one of the 2 connections live at one time, the first time you turn on 110V AC power and it feeds backwards into the DC system, there's going to be a noticeable smell of smoke and a boat full of things that don't work any more. If you can feed the AC power from your wind generator to the hot water element before it gets converted to DC, that would be safer but it means that the AC power from your boat could also electrify your wind generator and that's a bad idea too. So, in order to keep your AC and DC systems separate you need 2 separate elements. To do otherwise would be too expensive to do safely for very little gain and would be an invitation to disaster.
jtsailjt is offline   Reply With Quote
Old 02-03-2018, 08:27   #11
Registered User

Join Date: Aug 2016
Location: Vancouver
Boat: Farrier F-41
Posts: 26
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by SV FlyingSpirit View Post
Has anyone tried retrofitting a 120/240 VAC hot water tank with a DC element? I'm re-designing my solar system and adding a wind generator. Rather than shunting excess I think a better diversion would be heating water. Just curious if anyone else has tried it..
I am about to do this on my cat - although using 48v traction LiFePo4 banks.
Not very efficient to heat water; but the best way to use excess solar.
Missouri Wind & Solar (??) have both 12v. and 48v. replacement heater elements
that should fit most water tanks. They have some very informative how-to videos also.
Graham
Gmcgyvr is offline   Reply With Quote
Old 02-03-2018, 08:39   #12
Registered User
 
skipgundlach's Avatar

Join Date: Mar 2003
Location: Currently on the boat, somewhere on the ocean, living the dream
Boat: Morgan 461 S/Y Flying Pig
Posts: 2,298
Send a message via Skype™ to skipgundlach
Re: Using low-voltage water heating elements as a diversion load.

Dual (meaning you don't lose the ability to do AC heating) elements can work if the configuration of the tank allows. My current water heater does not, so I couldn't use the one I had in my Raritan, which did.

My vendor for that part was SVHotwire...

Divert Load FAQ – svHotWire
__________________
Morgan 461 #2 SV Flying Pig, KI4MPC
See our galleries at www.justpickone.org/skip/gallery!
skipgundlach is offline   Reply With Quote
Old 02-03-2018, 08:41   #13
Registered User
 
zboss's Avatar

Join Date: Sep 2011
Location: On a boat
Boat: 1987 Cabo Rico 38 #117 (sold) & 2008 Manta 42 #124
Posts: 4,174
Re: Using low-voltage water heating elements as a diversion load.

I think what appeals to me is just having the 12 volt element hooked directly to the batteries through the breaker panel. Turn it on when you have excess power available or if we absolutely need to run it at the same time as my honda generator is charging the batteries. It'll run fine off shore power obviously. No need to complicate the system by running more wires and worrying about diversion loads.
zboss is offline   Reply With Quote
Old 02-03-2018, 08:43   #14
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Using low-voltage water heating elements as a diversion load.

Quote:
Originally Posted by rom View Post
That's interesting, less current and less votage, yet the same power ... Can you show your calculation ?
You use I to the 5th power.
Cadence is offline   Reply With Quote
Old 02-03-2018, 08:48   #15
Registered User
 
skipgundlach's Avatar

Join Date: Mar 2003
Location: Currently on the boat, somewhere on the ocean, living the dream
Boat: Morgan 461 S/Y Flying Pig
Posts: 2,298
Send a message via Skype™ to skipgundlach
Re: Using low-voltage water heating elements as a diversion load.

Dual (meaning you don't lose the ability to do AC heating) elements can work if the configuration of the tank allows. My current water heater does not, so I couldn't use the one I had in my Raritan, which did.

My vendor for that part was SVHotwire...

Divert Load FAQ – svHotWire
__________________
Morgan 461 #2 SV Flying Pig, KI4MPC
See our galleries at www.justpickone.org/skip/gallery!
skipgundlach is offline   Reply With Quote
Reply

Tags
heating, loa, men, water

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Low Shorepower voltage with increased load? sailcrazy Electrical: Batteries, Generators & Solar 22 05-05-2016 04:57
Low voltage vs higer voltage solar Singleprop Electrical: Batteries, Generators & Solar 11 06-07-2015 19:35
For Sale: Diversion Load 12/24/48VDC Heater Elements osirissail Classifieds Archive 3 10-04-2015 21:47
Diversion Load for Wind Generator rnjpinz Electrical: Batteries, Generators & Solar 56 06-10-2014 11:30
Diversion Load Hkalan Electrical: Batteries, Generators & Solar 14 06-08-2013 00:37

Advertise Here


All times are GMT -7. The time now is 13:58.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.