We have a 18k cruisair reverse cycle a/c unit on our boat. Right now you hit cool and here a standard click from the unit (if memory serves me right we have always heard that click when the unit turns on) and about a second later a second click about 1-2 seconds later. The unit then appears to run but not pushing cold air and draw is only 2 amps. No air messages at all. We turn to heat and it seems to push heat.

In the past few months if the power dropped below 120v at all we would get lo ac message ad the unit would shut down. Also yesterday before the unit started not working right we powered off the unit at its control head and did the same to our rear ac unit and the water pump">raw water pump did not turn off. So after a while i turned the breakers off to the two units and the pump and to turn it off. Whe turned breakers on again pump works fine, but cant help but think this might be related.

Please if you have any ideas, as it is getting hot enough we really want our ac.

thanks in advance for your help
__________________

__________________
myisland is offline   Reply With Quote
Old 11-06-2012, 22:13   #2
Moderator
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 4,812
Re: Cruisair issue

How old is your shore power cord. I was getting a 10V drop with light load after 5 years. I cut the old shore plug and installed a new one and it was working with 0v drop again.

Could be the control relay messed up, which is my guess, with only 2 amps, the compressor is not running in cooling. So the control relay could have a burnt contact and might need replacing.

Have you checked your water flow???
__________________

__________________
sailorchic34 is offline   Reply With Quote
Old 12-06-2012, 10:56   #3
Registered User

Join Date: Jun 2012
Posts: 2
Re: Cruisair issue

Thanks for your help,
The shore power cord is only a year old but with bad power and a old boatside plug was starting to show as if it was getting hot on the plug so took the plug off the boat side end and hard wired it into the system and that gave us better power to the boat.

Any suggestions how to check the control relay? i have taken the covers off the two of the cruisair boxes with the unit and the circuit board was in one and looked great, wiring block in the other and it looked like new. someone also said locally a capacitor however i am not sure if it is the units placement or i am blind but i am not seeing anything that looks like a cap.

Water flow is excellent
__________________
myisland is offline   Reply With Quote
Old 12-06-2012, 11:27   #4
Registered User

Join Date: Dec 2009
Posts: 617
Re: Cruisair issue

do you have 2 identical units?
if so swap the control stuff around. If it has capacitors for starting -they will be large cylinders - few inches long - couple inches diameter. swap them to other unit. see if there is difference. sounds like the compressor is tripping on thermal overload - unfortunately may be seized - but if very lucky may be control item or low voltage from bad connection.
If works on heat - make sure is from compressor and not electrical booster element (if any) - and would be REALLY hot now...

Goes without saying you would have licensed electrician do this...
__________________
AllezCat is offline   Reply With Quote
Old 12-06-2012, 20:00   #5
Moderator
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 4,812
Re: Cruisair issue

The capacitor may be located on or adjacent to the compressor. Probablt 3-4 inches line and round or oval. Before touching it, and with power off (breaker in off) ground out between the two connections with an insulated handle screwdriver. Do not touch the capacitor till you ground out the charge.
__________________
sailorchic34 is offline   Reply With Quote
Old 12-06-2012, 20:03   #6
Moderator
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 4,812
Re: Cruisair issue

Its probably not a locked up compressor or capacitor btw as your amp load would still have been high. 2 amps when running says its a bad connection or control relay So your looking for the control relay, Should have the tstat wires connected to it
__________________
sailorchic34 is offline   Reply With Quote
Old 13-06-2012, 05:19   #7
Registered User

Join Date: Dec 2009
Posts: 617
Re: Cruisair issue

Quote:
Originally Posted by sailorchic34 View Post
Its probably not a locked up compressor or capacitor btw as your amp load would still have been high. 2 amps when running says its a bad connection or control relay So your looking for the control relay, Should have the tstat wires connected to it
"and about a second later a second click about 1-2 seconds later"
this is indicative of it locked up - drawing high amps - and tripping on the thermal overload.
If there is an amprobe on the compressor leads - it will show high amps then nothing when it trips.
I am assuming the 2 amps is read from typical boat amp display - and is from fan/pumps only...
but it could be anything...
__________________
AllezCat is offline   Reply With Quote
Old 13-06-2012, 16:38   #8
Moderator
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 4,812
Re: Cruisair issue

Could be. Having a helper turn the AC on while watching the amp load should show that bump for the lock rotor. A high voltage drop would cause the overload to trip too. Maybe change the high limit/ overload out as sometimes they go bad.... Or could be the capacitor as that would have similar effect.
__________________

__________________
sailorchic34 is offline   Reply With Quote
Reply

Tags
cruisair

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 10:48.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.