Condensate pan fills when AC unit is off

My condensate pan fills and overflows soon after opening the AC thru hull, even when the unit is off. Any ideas why that's happening?

I'm also working on figuring out why the drain hose isn't draining. But even if I solve that I need to fix the big problem if the condensate pan constantly filling.
nickfox45 is offline   Reply With Quote
Old 27-05-2017, 11:52   #2
Registered User

Join Date: Jul 2015
Location: Tonga
Boat: Tayana 48 DS
Posts: 40
Re: Condensate pan fills when AC unit is off

Is the water salty?
__________________
www.gadaboutlife.com
wagsea6b is offline   Reply With Quote
Old 27-05-2017, 12:43   #3
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Condensate pan fills when AC unit is off

there's a leak of course
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 27-05-2017, 12:45   #4
Registered User

Join Date: Oct 2013
Location: Maryland
Boat: Hunter 380
Posts: 89
Re: Condensate pan fills when AC unit is off

Quote:
Originally Posted by sailorboy1 View Post
there's a leak of course
Right! Any idea where?
nickfox45 is offline   Reply With Quote
Old 27-05-2017, 13:15   #5
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Condensate pan fills when AC unit is off

Quote:
Originally Posted by nickfox45 View Post
Right! Any idea where?
hose, hose connection, condenser tubing, ......................... have you looked as those are the choices?
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 27-05-2017, 13:16   #6
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Condensate pan fills when AC unit is off

is the seawater outlet open?

if closed maybe it is just the hose clamp
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 27-05-2017, 13:19   #7
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Condensate pan fills when AC unit is off

Follow the sea water travel, from the inlet, through the strainer, and up to the condenser assembly. The condenser is the copper tube coil that the sea water enters. Check the hose and clamp at the entry, as well as at the exit of the condenser. Your leak might be at the point(s) of connection.

If source not found at the connection points, feel around the coil for a wet spot. It is possible that the tubing could have ruptured if not properly winterized, or one of the brazed fittings might be leaking.

If still no smoking gun, confirm that the water accumulating in the pan is sea water. Oftentimes, the condensate pan is not properly sloped, or the drain has become clogged, and normal condensation from the evaporator coil is not being properly removed. In humid environments, condensation will also form on various components of the AC unit - refrigerant tubing, dryer, etc., in addition to the evaporator.

Report back on your findings for further steps to take, if source not found.
redsky49 is offline   Reply With Quote
Old 27-05-2017, 13:33   #8
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Condensate pan fills when AC unit is off

As a general maintenance item, the pan, as well as the evaporator coil face, the fan blades, etc., should be cleaned on a regular basis.

The challenge on a marine AC unit is access. It helps to have tiny hands (President Trump, where are you? ).

For the condensate pan, for example, it should be wiped down at least seasonally with an anti-microbial solution, removing all dirt and debris. Pan should be checked for level, corrosion and/or perforation and seam integrity (pans may be plastic, stainless, galvanized, etc.).

In the event that condensate pools in the unit, accumulated dust and dirt may float towards the drain opening, clogging it at the point of connection to the drain tube. These are typically only a 1/2" or 5/8" dia. opening, and can easily clog. If you can locate the condensate drain line, try blowing air back through the drain line in an attempt to dislodge any blockage. Perhaps you have a kink in the line, especially if using non-reinforced tubing.

Hope this gets you a start toward finding the problem.
redsky49 is offline   Reply With Quote
Old 27-05-2017, 18:23   #9
Registered User

Join Date: May 2017
Location: Katy, TX
Posts: 404
Re: Condensate pan fills when AC unit is off

It is possible that you are low on freon. When low, this causes the coils to actually freeze - you can see the ice. When off, the ice will melt, showing symptoms like you are seeing (assuming it's fresh water).
leboyd is offline   Reply With Quote
Old 28-05-2017, 05:48   #10
Registered User

Join Date: Oct 2013
Location: Maryland
Boat: Hunter 380
Posts: 89
Re: Condensate pan fills when AC unit is off

Quote:
Originally Posted by redsky49 View Post
Follow the sea water travel, from the inlet, through the strainer, and up to the condenser assembly. The condenser is the copper tube coil that the sea water enters. Check the hose and clamp at the entry, as well as at the exit of the condenser. Your leak might be at the point(s) of connection.

If source not found at the connection points, feel around the coil for a wet spot. It is possible that the tubing could have ruptured if not properly winterized, or one of the brazed fittings might be leaking.

If still no smoking gun, confirm that the water accumulating in the pan is sea water. Oftentimes, the condensate pan is not properly sloped, or the drain has become clogged, and normal condensation from the evaporator coil is not being properly removed. In humid environments, condensation will also form on various components of the AC unit - refrigerant tubing, dryer, etc., in addition to the evaporator.

Report back on your findings for further steps to take, if source not found.
Thanks for your suggestions. I've determined that the pan doesn't fill unless the seawater thru-hull is open, so I know it's not a freshwater leak. I traced the entry all the way to the condenser, but the inflow for that is below where I can see. I can't see or feel any obvious leaks from there.

If I turn on the unit, the pan will drain overboard thanks to the pump. For now, my plan is to just leave the thru-hull closed when the AC unit is not in use, so I can continue to troubleshoot.
nickfox45 is offline   Reply With Quote
Old 28-05-2017, 05:58   #11
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,614
Re: Condensate pan fills when AC unit is off

Depending on where the seawater leak is, there is a fair chance that it will get on something it should not and corrode the AC unit to trash in a season. Even when off, it will dry up to salt, which is worse.

You better find the leak and wash off the salt.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is offline   Reply With Quote
Old 28-05-2017, 13:46   #12
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Condensate pan fills when AC unit is off

Quote:
Originally Posted by nickfox45 View Post
My condensate pan fills and overflows soon after opening the AC thru hull, even when the unit is off. Any ideas why that's happening?

I'm also working on figuring out why the drain hose isn't draining. But even if I solve that I need to fix the big problem if the condensate pan constantly filling.
My dumb guess is an algae build up in your drain. A dose of Clorox once and awhile solves that.
Cadence is offline   Reply With Quote
Old 28-05-2017, 14:20   #13
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 666
Images: 5
Re: Condensate pan fills when AC unit is off

Tell us how your unit is configured. Our unit controls the raw water pump, so if the A/C is off, so is the pump. Our input thru hull is lowest (Below water line), then the pump (about at water line), then highest is the the coil (Above water line). Outflow is coil (highest) to output thru hull that is a few inches above the waterline.

Two issues I see: Where is the water coming from and how is it getting into the condensate pan?

Is the pan lower than the input thru-hull? Is the hose connection to the coil good and tight on both ends? (Inflow and Outflow) No tears or breaks in the hose at the end of the coil connections? Is the pan drain connected to the outflow thru hull? If so, is there a back-flow preventer or a siphon break? You could be siphoning water into the boat via the drain line from the outflow thru hull, or from the inflow if water pressure alone is filling the coil once you open the seacock. (How high is it compared to the water line?)

Hope you solve that mystery soon.
OS2Dude is offline   Reply With Quote
Old 28-05-2017, 17:24   #14
Registered User

Join Date: Jan 2015
Posts: 111
Re: Condensate pan fills when AC unit is off

Quote:
Originally Posted by nickfox45 View Post
My condensate pan fills and overflows soon after opening the AC thru hull, even when the unit is off. Any ideas why that's happening?

I'm also working on figuring out why the drain hose isn't draining. But even if I solve that I need to fix the big problem if the condensate pan constantly filling.
Good chance your unit is low on refrigerant. This would cause evap to freeze, hence when off, ice melts. Have HVAC Tech check charge.
icemate is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
PAN PAN....OR PON PON Mark1977 Our Community 249 15-07-2020 19:34
When to use Mayday-Pan-Pan and Securite ASD Health, Safety & Related Gear 0 20-10-2015 09:15
The trip... Securite.. as opposed to Pan Pan or Mayday.. blah blah blah boatman61 General Sailing Forum 281 15-04-2014 06:08
Condensate pan tablets batkins61 Plumbing Systems and Fixtures 0 24-11-2012 13:58

Advertise Here


All times are GMT -7. The time now is 08:10.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.