BD35 compressor not making frost on plate .

Good day .

Just replaced my evaporator plate 32x16 aluminum rollbond, with a new one on my Novakool air cooled bd235 compressor .
The unit has the self sealing connections so just bolted the new one on . The plate was precharged .

The plate gets cold and developed plenty of moisture on it but does not get cold enough to make frost on the surface. I hear a clear gurgling from the plate so I know there is flow .
The compressor is drawing way to many amps , 3.4 on low speed, but does not seem like it is struggling.

Would this do this if the plate came over charged ?

Thanks for any help
ColdEH is offline   Reply With Quote
Old 15-03-2016, 10:41   #2
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: BD35 compressor not making frost on plate .

Ah...but it's just a swap out. The plate comes vapor charged, which is not the same thing as being "charged", so when you removed the old plate you could have take out of the refrigeration loop more refrigerant than was in the replacement plate. Sounds to me like a classic symptom of an under charged unit.

If the system was overcharged, you would be seeing frost going back to the compressor, so the data point of not enough frost indicated a unit low on charge.

You have two ways to fix it.
1. The official way would be to vent off the refrigerant that is in there now and then charge with the exact amount the unit calls for.

2. or add refrigerant in 2-3 second spurts and then wait for 5 minutes and observe the frost line. You keep SLOWLY adding until you just start to see frost appearing on the copper return line exiting the evaporator and then let a spurt out. It can take a while to "blind balance" the charge like this, but it can be done. The KEY here is Patience and Going slow.
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 15-03-2016, 10:56   #3
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
Re: BD35 compressor not making frost on plate .

Hey Rich , thanks very much for the advice , I don't have my refill kit here with me at work , I have the unit sitting on my bench running off a battery.

I thought it seemed like a low charge but there was plenty of pressure behind the fill valve . The thing that was confusing me was the amps , 3.4 ?? seems like a lot .

I have it running now and watching it , tomorrow I will bring in my fill set and remove what is in the and add new stuff .

I will update with results .

Regards
ColdEH is offline   Reply With Quote
Old 15-03-2016, 11:21   #4
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,920
Re: BD35 compressor not making frost on plate .

3.4A doesn't sound too far off for the BD35....

So give us an update because we all learn from these types of things.
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 15-03-2016, 11:39   #5
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
BD35 compressor not making frost on plate .

Ok will do . Should be fun since I'm not doing this hanging upside down with myself jammed in a cupboard . This is easy 🤒
Regards

Sent from my iPhone using Cruisers Sailing Forum
ColdEH is offline   Reply With Quote
Old 15-03-2016, 11:43   #6
Registered User
 
leftbrainstuff's Avatar

Join Date: May 2011
Location: San Diego CA
Boat: Liberty 458
Posts: 2,205
Re: BD35 compressor not making frost on plate .

O
Quote:
Originally Posted by typhoon View Post
Good day .

Just replaced my evaporator plate 32x16 aluminum rollbond, with a new one on my Novakool air cooled bd235 compressor .
The unit has the self sealing connections so just bolted the new one on . The plate was precharged .

The plate gets cold and developed plenty of moisture on it but does not get cold enough to make frost on the surface. I hear a clear gurgling from the plate so I know there is flow .
The compressor is drawing way to many amps , 3.4 on low speed, but does not seem like it is struggling.

Would this do this if the plate came over charged ?

Thanks for any help
Several scenarios:[*] low on refrigerant[*] blocked capillary[*] compressor issue

Low charge is my first guess. What you're describing is not a symptom of overcharging.

Did you replace or add a filter dryer before installing the new evaporator? It's very easy to block the capillary when removing and replacing components.

You can fit a LED to check if compressor is fault free.

I'm in the process of switching out our evaporator which has a blocked capillary. Probably from a piece of thread locker from the self sealing fittings. Was fine for nearly 8 years.

I had to fit high and low pressure gauges to confirm a blockage. Gurgling was still evident. I could see the HP increase confirming a blockage.

Those self sealing fittings are a pain. Not having a filter dryer installed as standard before the capillary is stupid IMHO.

Sent from my SM-N900T using Cruisers Sailing Forum mobile app
leftbrainstuff is offline   Reply With Quote
Old 16-03-2016, 03:24   #7
Registered User
 
mayball's Avatar

Join Date: Jul 2008
Location: Puerto Vallarta, Mexico & Denver, Colorado
Boat: Sovereign, 28
Posts: 47
Re: BD35 compressor not making frost on plate .

The specs on the Danfoss BD35 for 2000 RPM and 0 degrees C is 4.0 amps.
mayball is offline   Reply With Quote
Old 16-03-2016, 03:55   #8
Now on the Dark Side: Stink Potter.
 
CSY Man's Avatar

Join Date: Aug 2003
Location: Palm Coast, Florida
Boat: Sea Hunt 234 Ultra
Posts: 3,971
Images: 124
Re: BD35 compressor not making frost on plate .

I averaged 5.0 amp/hrs on my BD35...
__________________
Life is sexually transmitted
CSY Man is offline   Reply With Quote
Old 16-03-2016, 08:14   #9
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: BD35 compressor not making frost on plate .

Quote:
Originally Posted by SV THIRD DAY View Post
Ah...but it's just a swap out. The plate comes vapor charged, which is not the same thing as being "charged", so when you removed the old plate you could have take out of the refrigeration loop more refrigerant than was in the replacement plate. Sounds to me like a classic symptom of an under charged unit.

If the system was overcharged, you would be seeing frost going back to the compressor, so the data point of not enough frost indicated a unit low on charge.

You have two ways to fix it.
1. The official way would be to vent off the refrigerant that is in there now and then charge with the exact amount the unit calls for.

2. or add refrigerant in 2-3 second spurts and then wait for 5 minutes and observe the frost line. You keep SLOWLY adding until you just start to see frost appearing on the copper return line exiting the evaporator and then let a spurt out. It can take a while to "blind balance" the charge like this, but it can be done. The KEY here is Patience and Going slow.
If he opted for 1, would he not have to pull a vacuum on it prior to charging?
Cadence is offline   Reply With Quote
Old 16-03-2016, 08:38   #10
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
Re: BD35 compressor not making frost on plate .

Thanks for all the replies. I have removed most of the gas and am about to refill . Don't think I will have to vacuum I didn't open any thing . How many onces do these things take to get me close ? My evaporate plate is a good size 32x16

Rdgards
ColdEH is offline   Reply With Quote
Old 16-03-2016, 09:34   #11
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: BD35 compressor not making frost on plate .

Quote:
Originally Posted by Cadence View Post
If he opted for 1, would he not have to pull a vacuum on it prior to charging?

No because pressure never gets to ambient so no way air could get in.
But since I over prepare everything, I'd want a drier in the system, and to do that you would have to open it up, sweat in the drier and pull a vacuum.
You can't pull too much vacuum nor can you leave the pump on too long either.

Oh and if you get a drier, be sure to get one with a sight glass
a64pilot is offline   Reply With Quote
Old 16-03-2016, 10:21   #12
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
Re: BD35 compressor not making frost on plate .

I have it up and running . I don't think I have the charge right . The evaporator is siting outside a box on a bench , would it still frost all up in the open air ? Right now it is running at 7psi for the last twenty minutes.
Compressor is just slightly warm and the condenser tubes and fins are cool.

Regards
ColdEH is offline   Reply With Quote
Old 16-03-2016, 10:30   #13
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: BD35 compressor not making frost on plate .

Quote:
Originally Posted by a64pilot View Post
No because pressure never gets to ambient so no way air could get in.
But since I over prepare everything, I'd want a drier in the system, and to do that you would have to open it up, sweat in the drier and pull a vacuum.
You can't pull too much vacuum nor can you leave the pump on too long either.

Oh and if you get a drier, be sure to get one with a sight glass
I think I would try opt. 2. It is probably the same a conventional. Charge until the line frosts and bleed off till the isn't?
Cadence is offline   Reply With Quote
Old 16-03-2016, 10:39   #14
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
Re: BD35 compressor not making frost on plate .

Quote:
Originally Posted by Cadence View Post
I think I would try opt. 2. It is probably the same a conventional. Charge until the line frosts and bleed off till the isn't?
I have about 12 inches of frost running down the pipes from the evaporator , but the entire plate is not frosted , still running at 7.5 psi .

Regards
ColdEH is offline   Reply With Quote
Old 16-03-2016, 10:39   #15
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: BD35 compressor not making frost on plate .

It will frost up in open air, unless of course open air is not a 100 deg day and a 20 MPH wind or something, but in a shop, yes.
a64pilot is offline   Reply With Quote
Reply

Tags
compressor


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Sea Frost Refrigeration - DC5000 compressor bluewaterbill Classifieds Archive 0 17-03-2015 07:58
Danfoss bd35 compressor economy mode Dod42 Electrical: Batteries, Generators & Solar 14 10-07-2014 06:18
Danfoss BD35/Frigoboat problem hoaga Plumbing Systems and Fixtures 87 27-02-2014 19:57
Free: Sea Frost. Engine Compressor Holding Plate etc. Free Tellie Classifieds Archive 2 12-10-2010 13:59
Danfoss BD35 Celestialsailor Plumbing Systems and Fixtures 2 24-11-2006 14:16

Advertise Here


All times are GMT -7. The time now is 22:16.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.